110 wiring in 220 AC Disconnect Box
#1
Member
Thread Starter
Join Date: Jul 2014
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
110 wiring in 220 AC Disconnect Box
Wiring a 110v Sanyo Split AC system. Couldn't locate a 110 Disconnect box so using a 220v one.
The 220v one has 2 sets of line/load terminals for the normal 2 black hot wires to make up normal 220v's…… and a ground lug below the above line/load pull disconnect terminals for the bare ground.
For wiring in a 220 unit this is pretty straight forward…..The 2 line blacks in and 2 load blacks out with the bare ground to ground lug. NO white neutral involved.
BUT the question is… When using this box for a 110 hookup (1 blk, 1 white and 1 bare ground) how do you wire. HDepot guy told me to just use one side of the pull disconnect terminals for the black and hook the 2 grounds and two white neutrals to the ground lug…. Suspect this will work functionally but doubt it's code.
Should I instead connect the black to one line/load side of the pull disconnect and the white neutral to the other side so that when the disconnect is pulled then both the black and white side are disconnected………????
I don't really want to go out and find a 110 disconnect box!
What do u think??
b…
I'll try to attach a pic but never did this before so may not work. Hope words are clear enough…….IMG_20140723_214146_395.jpg
The 220v one has 2 sets of line/load terminals for the normal 2 black hot wires to make up normal 220v's…… and a ground lug below the above line/load pull disconnect terminals for the bare ground.
For wiring in a 220 unit this is pretty straight forward…..The 2 line blacks in and 2 load blacks out with the bare ground to ground lug. NO white neutral involved.
BUT the question is… When using this box for a 110 hookup (1 blk, 1 white and 1 bare ground) how do you wire. HDepot guy told me to just use one side of the pull disconnect terminals for the black and hook the 2 grounds and two white neutrals to the ground lug…. Suspect this will work functionally but doubt it's code.
Should I instead connect the black to one line/load side of the pull disconnect and the white neutral to the other side so that when the disconnect is pulled then both the black and white side are disconnected………????
I don't really want to go out and find a 110 disconnect box!
What do u think??
b…
I'll try to attach a pic but never did this before so may not work. Hope words are clear enough…….IMG_20140723_214146_395.jpg
#2
Forum Topic Moderator
Almost correct, but not quite.
You want to remove the white wires from the ground block and wire nut them together. Blacks stay as-is and grounds stay in the ground block.
Neutrals and grounds can only be connected in the main panel, everywhere else they must remain separate.
No need to find a 120v disconnect box. Though next time, you could use a standard box (outdoor if necessary) and a toggle switch. It looks like a 15 or 20A circuit, so a standard toggle switch would have been fine.
You want to remove the white wires from the ground block and wire nut them together. Blacks stay as-is and grounds stay in the ground block.
Neutrals and grounds can only be connected in the main panel, everywhere else they must remain separate.
No need to find a 120v disconnect box. Though next time, you could use a standard box (outdoor if necessary) and a toggle switch. It looks like a 15 or 20A circuit, so a standard toggle switch would have been fine.
#4
Makes sense to do that rather than breaking a neutral (backup
ground basically).
ground basically).
Tech note: You have 120 volts not 110. That is a 240 volt disconnect not 220.
Last edited by ray2047; 07-24-14 at 01:33 PM.