NEC Pull body questions

I am running a sub panel in a detached garage using 4 xhhw and 1" conduit the whole way. I know this meets the requirement for conduit fill but in hind sight at least 1 1/4 would have been a better choice.

My question is related to 300.4(G). Does this requirement apply to LB's and would the following meet the requirement?

Also should i be concerned with the bend radius in a 1" LB?

Shop Gampak 1-in Rigid Bushing at Lowes.com

or

Shop CANTEX 1-in Schedule 40 PVC Adaptor at Lowes.com
 
Sponsored Links
  #2  
Old 08-06-14, 01:46 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 46,213
You can fit up to four #4 wires in a 1" pipe.

300.4(G) states that you need to use bushings on conduits/fittings where #4 or larger wires are present.
So yes.... you need to use a 1" bushing on the fittings where they enter the panel.


I'm not sure why you've listed a PVC reducing bushing here.

This is the adapter/connector used to connect 1" PVC conduit to a panel. You would use a locknut and a bushing on it.

Name:  pvc.jpg
Views: 83
Size:  4.1 KB
 
  #3  
Old 08-06-14, 08:42 AM
Member
Join Date: Jul 2014
Location: usa
Posts: 279
Shop CANTEX 1-in Schedule 40 PVC Adaptor at Lowes.com
this is not a PVC reducing bushing ...............it is a PVC slip chase nipple. doesnot takeup much space in the box.

it works very good where you are connecting a pipe you canot move to a box you canot move. run your pipe to the box...end it with a coupling tight on the outside of the box...the box adaptor is glued in from inside the box.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes