Washer Dryer: Separate Circuit?
#1
Member
Thread Starter
Join Date: Apr 2009
Location: Burien, WA
Posts: 93
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Washer Dryer: Separate Circuit?
Do washers and dryers (gas 120V variety) need their own circuits?
#3
Laundry Branch Circuit. One 20 ampere branch circuit is required for the laundry room receptacle outlet(s) [210-52(f)]. The laundry room receptacle circuit cannot serve any other outlet, such as the laundry room lighting or receptacles in other rooms.
#7
Member
Thread Starter
Join Date: Apr 2009
Location: Burien, WA
Posts: 93
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It looks like my municipality is using the 2008 code, so hopefully I can avoid that.
In my other thread I ran a circuit to the laundry room but terminated it at a surface mount, plastic two-gang box. I was thinking of extending the power to the washing machine but I don't know what the best way to do this. There is brick under the box so I can't go through the wall. I could do one of three things:
Use plastic conduit from the new box and surface mount it down the wall and extend it to the middle of the adjacent wall (that would end up being three 90• bends) and terminate at another surface mount box.
Use plastic conduit from the new box and surface mount it, run it into the adjacent wall, fish it through the wall and use the existing in-wall box.
Run the circuit from the laundry room box, back into the dining room wall, then into the crawl back up into the existing in-wall box.
In my other thread I ran a circuit to the laundry room but terminated it at a surface mount, plastic two-gang box. I was thinking of extending the power to the washing machine but I don't know what the best way to do this. There is brick under the box so I can't go through the wall. I could do one of three things:
Use plastic conduit from the new box and surface mount it down the wall and extend it to the middle of the adjacent wall (that would end up being three 90• bends) and terminate at another surface mount box.
Use plastic conduit from the new box and surface mount it, run it into the adjacent wall, fish it through the wall and use the existing in-wall box.
Run the circuit from the laundry room box, back into the dining room wall, then into the crawl back up into the existing in-wall box.
#8
Member
Join Date: Jul 2014
Location: usa
Posts: 258
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I just read on the Holt forums that GFCI and AFCI is required in laundry rooms. Is that accurate?
210.8 (A) (10) for GFCI
MY READING OF NEC 2014 210.8 many outlets that must GFCI PROTECTED.
my reading of NEC 2014 210.12 all.... every ... 120 volt,single phase,15 or 20 amp branch circuits supplying outlets or devices ..must be arc-fault protected.
can anyone spot a room that must not have arc-fault protection?
#10
Member
Thread Starter
Join Date: Apr 2009
Location: Burien, WA
Posts: 93
Upvotes: 0
Received 0 Upvotes
on
0 Posts
With the two new arc fault interrupters and the two existing GFI breakers my panel is starting to feel full...
I'm going to skip extending the circuit this time around, but I would still like opinions on the surface mount conduit ideas.
I'm going to skip extending the circuit this time around, but I would still like opinions on the surface mount conduit ideas.
#12
Member
Join Date: Jul 2013
Location: USA
Posts: 57
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'd say go with an external conduit like you planned, the choice of conduit is asthetic based on your preferences.
As far as AFCI:
210.12 Arc-Fault Circuit-Interrupter Protection.
(A) Dwelling Units. All 120-volt, single phase, 15- and
20-ampere branch circuits supplying outlets installed in
dwelling unit family rooms, dining rooms, living rooms,
parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, or similar rooms or areas shall
be protected by a listed arc-fault circuit interrupter,
combination-type, installed to provide protection of the
branch circuit.
I don't see kitchens, baths, garages, basements, outdoors... Seems like anyone who gets a GFCI doesn't require AFCI. I wonder if it's even possible to trip an AFCI before a GFCI??
As far as AFCI:
210.12 Arc-Fault Circuit-Interrupter Protection.
(A) Dwelling Units. All 120-volt, single phase, 15- and
20-ampere branch circuits supplying outlets installed in
dwelling unit family rooms, dining rooms, living rooms,
parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, or similar rooms or areas shall
be protected by a listed arc-fault circuit interrupter,
combination-type, installed to provide protection of the
branch circuit.
I don't see kitchens, baths, garages, basements, outdoors... Seems like anyone who gets a GFCI doesn't require AFCI. I wonder if it's even possible to trip an AFCI before a GFCI??
#13
AFCI and GFCI look at different characteristics before tripping. The purposes are entirely different.
#14
I don't see kitchens, baths, garages, basements, outdoors... Seems like anyone who gets a GFCI doesn't require AFCI. I wonder if it's even possible to trip an AFCI before a GFCI??
I just recently read something on kitchen AFCI requirements on Code Question of the Day and just found it.
http://www.neca-neis.org/cqd/index.c...estion&id=4584
Last edited by CasualJoe; 08-07-14 at 07:43 PM.
#15
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
I think it highly unlikely that Devin's locale is under the 2008 NEC as Washington state has adopted the 2011 code. It may have also adopted the 2014 code as this state seems to adopt every model code as soon as it is issued. It is more likely that his location simply hasn't updated their municipal code statutes for a long time.
#16
I remember something about a change in the 2014 for many circuits but don't remember the specific requirements.
#18
Member
Something that caught my attention that I think Devin is missing here in the replies that he has been given.
He states :
If I am interpreting what Devin is saying he is going against code. He ran a new circuit to a 2 gang box (assuming there will be receptacles in this two gang box) and then extending that circuit to another receptacle where he will be plugging in a washing machine. If he is extending the circuit to another receptacle then he is against code because there are more than one receptacle on the laundry circuit.
He states :
In my other thread I ran a circuit to the laundry room but terminated it at a surface mount, plastic two-gang box. I was thinking of extending the power to the washing machine but I don't know what the best way to do this.
#19
Member
Join Date: Jul 2014
Location: usa
Posts: 258
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If he is extending the circuit to another receptacle then he is against code because there are more than one receptacle on the laundry circuit.
#20
The laundry circuit is limited to the laundry area. The code does not require this to only be one receptacle, it just cannot serve other areas.
#22
The proof is in the plural....................
(2) Laundry Branch Circuits. In addition to the number
of branch circuits required by other parts of this section, at
least one additional 20-ampere branch circuit shall be provided
to supply the laundry receptacle outlet(s) required by
210.52(F). This circuit shall have no other outlets.
210.52(F) Laundry Areas. In dwelling units, at least one receptacle
outlet shall be installed for the laundry.
(2) Laundry Branch Circuits. In addition to the number
of branch circuits required by other parts of this section, at
least one additional 20-ampere branch circuit shall be provided
to supply the laundry receptacle outlet(s) required by
210.52(F). This circuit shall have no other outlets.
210.52(F) Laundry Areas. In dwelling units, at least one receptacle
outlet shall be installed for the laundry.