Washer Dryer: Separate Circuit?

Do washers and dryers (gas 120V variety) need their own circuits?
 
  #2  
Old 08-06-14, 07:10 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Devin, when you have a new question please start a new thread. It's too confusing when you piggyback. I have moved your post to its own thread.
 
  #3  
Old 08-06-14, 07:19 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Laundry Branch Circuit. One 20 ampere branch circuit is required for the laundry room receptacle outlet(s) [210-52(f)]. The laundry room receptacle circuit cannot serve any other outlet, such as the laundry room lighting or receptacles in other rooms.
Source:Mike Holt Mike Holt Code Resources Code Tips
 
  #4  
Old 08-06-14, 07:32 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,937
Received 181 Upvotes on 159 Posts
To add GFI protection is required within 6' of a sink.
 
  #5  
Old 08-06-14, 10:33 AM
D
Member
Thread Starter
Join Date: Apr 2009
Location: Burien, WA
Posts: 93
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yeah, no sinks in there. I just read on the Holt forums that GFCI and AFCI is required in laundry rooms. Is that accurate?
 
  #6  
Old 08-06-14, 10:43 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,937
Received 181 Upvotes on 159 Posts
That sounds like the change made by the 2014 edition of the NEC.
 
  #7  
Old 08-06-14, 03:31 PM
D
Member
Thread Starter
Join Date: Apr 2009
Location: Burien, WA
Posts: 93
Upvotes: 0
Received 0 Upvotes on 0 Posts
It looks like my municipality is using the 2008 code, so hopefully I can avoid that.

In my other thread I ran a circuit to the laundry room but terminated it at a surface mount, plastic two-gang box. I was thinking of extending the power to the washing machine but I don't know what the best way to do this. There is brick under the box so I can't go through the wall. I could do one of three things:

Use plastic conduit from the new box and surface mount it down the wall and extend it to the middle of the adjacent wall (that would end up being three 90• bends) and terminate at another surface mount box.

Use plastic conduit from the new box and surface mount it, run it into the adjacent wall, fish it through the wall and use the existing in-wall box.

Run the circuit from the laundry room box, back into the dining room wall, then into the crawl back up into the existing in-wall box.
 
  #8  
Old 08-07-14, 12:41 AM
J
Member
Join Date: Jul 2014
Location: usa
Posts: 258
Upvotes: 0
Received 0 Upvotes on 0 Posts
I just read on the Holt forums that GFCI and AFCI is required in laundry rooms. Is that accurate?
yes....210.12 (A) for arc-fault

210.8 (A) (10) for GFCI

MY READING OF NEC 2014 210.8 many outlets that must GFCI PROTECTED.

my reading of NEC 2014 210.12 all.... every ... 120 volt,single phase,15 or 20 amp branch circuits supplying outlets or devices ..must be arc-fault protected.

can anyone spot a room that must not have arc-fault protection?
 
  #9  
Old 08-07-14, 05:39 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,159
Received 814 Upvotes on 685 Posts
Bathrooms are still not required to have arc fault protection. Neither is garages, unfinished spaces, or anyplace not in a dwelling.
 
  #10  
Old 08-07-14, 10:58 AM
D
Member
Thread Starter
Join Date: Apr 2009
Location: Burien, WA
Posts: 93
Upvotes: 0
Received 0 Upvotes on 0 Posts
With the two new arc fault interrupters and the two existing GFI breakers my panel is starting to feel full...

I'm going to skip extending the circuit this time around, but I would still like opinions on the surface mount conduit ideas.
 
  #11  
Old 08-07-14, 11:46 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,842
Received 179 Upvotes on 162 Posts
210.8 (A) (10) for GFCI
There is no (10) under 210.8 (A) in the 2008 NEC which is the version adopted by the OP's municipality.
 
  #12  
Old 08-07-14, 02:15 PM
M
Member
Join Date: Jul 2013
Location: USA
Posts: 57
Upvotes: 0
Received 0 Upvotes on 0 Posts
I'd say go with an external conduit like you planned, the choice of conduit is asthetic based on your preferences.

As far as AFCI:
210.12 Arc-Fault Circuit-Interrupter Protection.
(A) Dwelling Units. All 120-volt, single phase, 15- and
20-ampere branch circuits supplying outlets installed in
dwelling unit family rooms, dining rooms, living rooms,
parlors, libraries, dens, bedrooms, sunrooms, recreation
rooms, closets, hallways, or similar rooms or areas shall
be protected by a listed arc-fault circuit interrupter,
combination-type, installed to provide protection of the
branch circuit.

I don't see kitchens, baths, garages, basements, outdoors... Seems like anyone who gets a GFCI doesn't require AFCI. I wonder if it's even possible to trip an AFCI before a GFCI??
 
  #13  
Old 08-07-14, 03:58 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,937
Received 181 Upvotes on 159 Posts
AFCI and GFCI look at different characteristics before tripping. The purposes are entirely different.
 
  #14  
Old 08-07-14, 06:56 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,842
Received 179 Upvotes on 162 Posts
I don't see kitchens, baths, garages, basements, outdoors... Seems like anyone who gets a GFCI doesn't require AFCI. I wonder if it's even possible to trip an AFCI before a GFCI??
I believe the 2014 NEC requires small appliance branch circuits to be AFCI protected and the small appliance branch circuit receptacles (on those circuits) to be GFCI protected.

I just recently read something on kitchen AFCI requirements on Code Question of the Day and just found it.

http://www.neca-neis.org/cqd/index.c...estion&id=4584
 

Last edited by CasualJoe; 08-07-14 at 07:43 PM.
  #15  
Old 08-07-14, 07:09 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
I think it highly unlikely that Devin's locale is under the 2008 NEC as Washington state has adopted the 2011 code. It may have also adopted the 2014 code as this state seems to adopt every model code as soon as it is issued. It is more likely that his location simply hasn't updated their municipal code statutes for a long time.
 
  #16  
Old 08-07-14, 07:10 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,937
Received 181 Upvotes on 159 Posts
I remember something about a change in the 2014 for many circuits but don't remember the specific requirements.
 
  #17  
Old 08-08-14, 09:50 AM
D
Member
Thread Starter
Join Date: Apr 2009
Location: Burien, WA
Posts: 93
Upvotes: 0
Received 0 Upvotes on 0 Posts
According to the website for my city they are still on the 2008 code. I guess I'll find out once I get my inspection on Tuesday.
 
  #18  
Old 08-09-14, 05:31 AM
A
Member
Join Date: Mar 2014
Posts: 955
Received 152 Upvotes on 127 Posts
Something that caught my attention that I think Devin is missing here in the replies that he has been given.

He states :
In my other thread I ran a circuit to the laundry room but terminated it at a surface mount, plastic two-gang box. I was thinking of extending the power to the washing machine but I don't know what the best way to do this.
If I am interpreting what Devin is saying he is going against code. He ran a new circuit to a 2 gang box (assuming there will be receptacles in this two gang box) and then extending that circuit to another receptacle where he will be plugging in a washing machine. If he is extending the circuit to another receptacle then he is against code because there are more than one receptacle on the laundry circuit.
 
  #19  
Old 08-09-14, 05:38 AM
J
Member
Join Date: Jul 2014
Location: usa
Posts: 258
Upvotes: 0
Received 0 Upvotes on 0 Posts
If he is extending the circuit to another receptacle then he is against code because there are more than one receptacle on the laundry circuit.
you may have more then one receptacle on the laundry circuit.must all be in laundry
 
  #20  
Old 08-09-14, 05:39 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,937
Received 181 Upvotes on 159 Posts
The laundry circuit is limited to the laundry area. The code does not require this to only be one receptacle, it just cannot serve other areas.
 
  #21  
Old 08-09-14, 05:43 AM
A
Member
Join Date: Mar 2014
Posts: 955
Received 152 Upvotes on 127 Posts
Oh, okay, "my bad". My misinterpretation
 
  #22  
Old 08-09-14, 05:45 AM
bigboypete's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2013
Posts: 201
Upvotes: 0
Received 0 Upvotes on 0 Posts
The proof is in the plural....................

(2) Laundry Branch Circuits. In addition to the number
of branch circuits required by other parts of this section, at
least one additional 20-ampere branch circuit shall be provided
to supply the laundry receptacle outlet(s) required by
210.52(F). This circuit shall have no other outlets.

210.52(F) Laundry Areas. In dwelling units, at least one receptacle
outlet shall be installed for the laundry.
 
 