New 100A sub panel questions on gauge and codes.
#1
Member
Thread Starter
Join Date: Aug 2014
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
New 100A sub panel questions on gauge and codes.
I have a 200A main panel on my house built in 1991. It's totally full, but i changed to a gas stove so I could remove a 40A 220 breaker. There is another 30A 220 drier outlet that I dont use because I have a gas drier. I figure that it would be fine to remove both of those and replace them with a 70A feed to a new workshop that I'm building. I'm hoping that I could add 100A instead because the reality is that the house breakers are way overkill for most rooms. I think every room is on it's own circuit (there are 30 breakers!) Going to a 400A panel is not in my budget because I need larger conduit off the main drop, new concrete, etc, and I'll never come close to pulling 200A.
I have a number of 220V tools, but they will never be used at the same time because it's just me in there. I have an old welder that can pull 80A @220v, but that is for welding 1" and I probably wont do that. I ran everything at my last house on a 40A circuit and I never popped it. I will also have a 40A on demand hot water heater that will provide hot water to the shop. The other 220v tools are another welder, vacuum, table saw, and a car lift.
Someone told me that I could run some kind of wire that comes in conduit under the house. I'm wondering if I even need conduit under the house. The rest of the large wires under there are not in conduit.
- Does anyone see any problem with running a 100A breaker to replace a 40 and 30A?
I have a number of 220V tools, but they will never be used at the same time because it's just me in there. I have an old welder that can pull 80A @220v, but that is for welding 1" and I probably wont do that. I ran everything at my last house on a 40A circuit and I never popped it. I will also have a 40A on demand hot water heater that will provide hot water to the shop. The other 220v tools are another welder, vacuum, table saw, and a car lift.
Someone told me that I could run some kind of wire that comes in conduit under the house. I'm wondering if I even need conduit under the house. The rest of the large wires under there are not in conduit.
- Is there some sort of newer code that requires conduit under the house?
- It seems that the length of the run doesn't matter for the wire gauge with AC. Is that true?
- I was thinking about running 4 x 2 gauge wire (2 hots, neutral and ground). Is that too much, or not enough gauge?
- What size conduit should I run underground? I assume PVC is ideal. True?
#2
Welcome to the forums.
How do you run conduit UNDER the house ?
Most times it's run around the house. PVC conduit is fine.
You can put a 100A two pole breaker in place of one of the non-used breakers.
How do you run conduit UNDER the house ?
Most times it's run around the house. PVC conduit is fine.
You can put a 100A two pole breaker in place of one of the non-used breakers.
#4
Member
Join Date: Jul 2014
Location: usa
Posts: 258
Upvotes: 0
Received 0 Upvotes
on
0 Posts
your 200 amp service should be fine.
no
no.....................but pvc conduit is very nice.
..........pvc conduit all the way with THHN wire...hang the pipe under the house..........
.3#4 and 1#6 ground go underground as you leave the house......no J-BOX.....1 1/4 or 1 1/2 inch pipe.
run the 4-wire circuit to a sub panel in the shop.
Does anyone see any problem with running a 100A breaker to replace a 40 and 30A?
Is there some sort of newer code that requires conduit under the house?
..........pvc conduit all the way with THHN wire...hang the pipe under the house..........
.3#4 and 1#6 ground go underground as you leave the house......no J-BOX.....1 1/4 or 1 1/2 inch pipe.
run the 4-wire circuit to a sub panel in the shop.
#5
pvc conduit all the way with THHN wire...hang the pipe under the house..........
.3#4 and 1#6 ground go underground as you leave the house......no J-BOX.....1 1/4 or 1 1/2 inch pipe.
run the 4-wire circuit to a sub panel in the shop
.3#4 and 1#6 ground go underground as you leave the house......no J-BOX.....1 1/4 or 1 1/2 inch pipe.
run the 4-wire circuit to a sub panel in the shop
For a 100 amp feeder to the garage, I'd use either 3 - #3 copper THHN/THWN and 1 - #8 copper THHN/THWN ground....OR....3 - #1 aluminum XHHW and 1 - #6 aluminum XHHW ground in 1 1/2" conduit.