Hi i just wanted to double check on something im having done to a crawlspace area and reconfirm a few things.
When having a sump pump installed is it required to have gfci outlet or hard wired to gfci breaker?
Also is it required to have a on/off switch if it is on a gfci outlet in crawlspace, and can it be tied into living room circuit or is it required to be on its own circuit?
Any additional info is appreciated !
Old 08-07-14, 10:01 AM
Tolyn Ironhand's Avatar
Received 881 Upvotes on 744 Posts
The sump pump is required to be GFCI protected. A breaker, or a GFCI device, someplace convenient might be better then a GFCI receptacle in the crawlspace by the pump.
Sump pumps normally have a cord and plug that is considered a disconnect so no switch is required. It could be tied into the living room circuit depending on the current load on that circuit. You don't want to overload that circuit but only you can determine that.
Old 08-07-14, 03:21 PM
bigboypete's Avatar
Although not required, most certainly put the pump on its own circuit.... it will be no fun watching your lights dim in your living room every time it operates.
Old 08-11-14, 10:31 AM
T
~an electrician will be doing it.its under a condo so im sure He wont be putting it on the same circuit as lights,i believe my lights are on a 15amp anyway.the closest circuit to the pump is a 20 amp for living room outlets with not a lot of load on it.Ill try to get it set up on that with a gfci inside at plug before it or i Gfci breaker
If i were doing it of coarse running a seperate gfci protected circuit would be ideal,but im not ,
~but i want to be sure it is done up to code,and hopefully not a gfci outlet in the hard to get to crawlspace ,should it need a reset.
thanks!
Old 08-11-14, 10:49 AM
NEC 2014 620.85 Ground-Fault Circuit-Interrupter Protection for
Personnel. Each 125-volt, single-phase, 15- and 20-ampere
receptacle installed in pits, in hoistways, on elevator car
tops, and in escalator and moving walk wellways shall be
of the ground-fault circuit-interrupter type.
All 125-volt, single-phase, 15- and 20-ampere recep-
tacles installed in machine rooms and machinery spaces
shall have ground-fault circuit- interrupter protection for
personnel.
A single receptacle supplying a permanently installed
sump pump shall not require ground-fault circuit-
interrupter protection.
Mod Note: the title of Article 620 is for elevators, dumbwaiters, escalators, moving walks etc. None of this article can be used in regards to a sump pump in a crawlspace.
Old 08-11-14, 11:46 AM
ray2047's Avatar
Good find John but the question would be if the AHJ considered a residential basement a machinery space.
Old 08-11-14, 12:54 PM
bigboypete's Avatar
gfci is required. The OP is installing the pump in his crawlspace. You cant tap dance around that fact.
In addition, the OP's electrician should be selling a new circuit here.... no way would I want a sump pump sharing a circuit no matter how light of a load is on that circuit.
Old 08-11-14, 06:56 PM
CasualJoe's Avatar
Received 185 Upvotes on 166 Posts
The code danced around the GFCI requirement for several years, but I am pretty sure the 2008 NEC clarified that sump pumps must have GFCI protection. I haven't looked it up, but I may later if I get to it.
Old 08-11-14, 07:32 PM
pcboss's Avatar
Received 196 Upvotes on 172 Posts
The single receptacle exception from GFI protection was removed. All receptacles in the crawlspace require GFI protection if 15 or 20 amp, 120 volt.