Looking for some advice.
I am going to be running two new 20A circuits using two 12/2 romex runs in my basement across the ceiling joists. Then I am going to run them down a masonry wall with both in a single piece of 1" EMT and then terminate them into a single 2-gang box with two 20A GFI receptacles.
My understanding is that I need to (or should) convert the romex to THHN before it enters the EMT. My question is, how do I convert it? I was planning on installing a handy box, but I don't know what to use to join the romex wires to the THHN wires. Can you even use wirenuts for a 20A load?
Also, is there anything I should take into account because the masonry is a cinder block wall with earth on the other side? Any corrosion issues I should be aware of? I was planning on mounting the hole straps with standard Tapcon screws.
btw, the use of EMT is only for protection against physical damage. Thanks.
I am going to be running two new 20A circuits using two 12/2 romex runs in my basement across the ceiling joists. Then I am going to run them down a masonry wall with both in a single piece of 1" EMT and then terminate them into a single 2-gang box with two 20A GFI receptacles.
My understanding is that I need to (or should) convert the romex to THHN before it enters the EMT. My question is, how do I convert it? I was planning on installing a handy box, but I don't know what to use to join the romex wires to the THHN wires. Can you even use wirenuts for a 20A load?
Also, is there anything I should take into account because the masonry is a cinder block wall with earth on the other side? Any corrosion issues I should be aware of? I was planning on mounting the hole straps with standard Tapcon screws.
btw, the use of EMT is only for protection against physical damage. Thanks.
#2
You make the transition in a permanently accessible junction box and secure the splices with the appropriate wire nut twist-on connector. I believe the red ones from most manufacturers would work fine. OR....since the EMT is just for physical protection and just a protective sleeve, just route the 2 NM-B cable (aka romex) down the conduit into the box and don't have the hassle of a junction box.
Why are you going to the extra expense of 20 amp GFCI receptacles when all you need is 15 amp rated devices? By the way, current code requires the 2 new circuits to be AFCI protected and the GFCI receptacles to be tamper resistant.
terminate them into a single 2-gang box with two 20A GFI receptacles.
#3
Member
Thread Starter
Join Date: Aug 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It's for running a chest freezer and a refrigerator, each requiring a 20A circuit.
Will I need to increase the diameter of the EMT conduit to take into account for conduit fill %?
Our home was built in 2003 and there are AFCI breakers for the bedrooms, are AFCI breakers a requirement for most new circuits?
Also, is this what you're talking about (for a CH style box)? - Eaton Type Ch 20 Amp Combination Arc Fault Circuit Breaker
Will I need to increase the diameter of the EMT conduit to take into account for conduit fill %?
Our home was built in 2003 and there are AFCI breakers for the bedrooms, are AFCI breakers a requirement for most new circuits?
Also, is this what you're talking about (for a CH style box)? - Eaton Type Ch 20 Amp Combination Arc Fault Circuit Breaker
#5
By the way, current code requires the 2 new circuits to be AFCI protected and the GFCI receptacles to be tamper resistant.
#6
Member
Thread Starter
Join Date: Aug 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I thought all receptacles had to be TR and AFCI was required for all living spaces. Is the basement finished?
So the chest freezer can be a 15A circuit, but does the fridge still need a 20A circuit?
#7
The price is the same for a 15 and 20 amp breaker. You already ran the wire to support the 20 amp circuit.
Since this mix unfinished you do need GFI protection.
Since this mix unfinished you do need GFI protection.
#8
Member
Thread Starter
Join Date: Aug 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The price is the same for a 15 and 20 amp breaker. You already ran the wire to support the 20 amp circuit.
Can I get away with 6 conductors in 1" EMT?
#9
You cannot use #14 on 20 amp circuits.
You can just sleeve the NM down the conduit without a junction box. Use a bushing at the top of the sleeve.
You can just sleeve the NM down the conduit without a junction box. Use a bushing at the top of the sleeve.
#10
Member
Join Date: Jul 2014
Location: usa
Posts: 258
Upvotes: 0
Received 0 Upvotes
on
0 Posts
if you go to all the work to pull 2 cables.....pull 12-2 wg on 20 amp breakers ............with 2 pvc conduits for protection against physical damage going to 2 boxes.use the gray pve outdoor boxes for a clean look.
You can just sleeve the NM down the conduit without a junction box.
You can just sleeve the NM down the conduit without a junction box.
#11
Member
Thread Starter
Join Date: Aug 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
You cannot use #14 on 20 amp circuits.
You can just sleeve the NM down the conduit without a junction box. Use a bushing at the top of the sleeve.
You can just sleeve the NM down the conduit without a junction box. Use a bushing at the top of the sleeve.
So I can run 2 lengths of 12/2 romex down a single piece of 1" EMT and not need to worry about heat buildup or whatever? I just want to be sure. Thanks.
if you go to all the work to pull 2 cables.....pull 12-2 wg on 20 amp breakers ............with 2 pvc conduits for protection against physical damage going to 2 boxes.use the gray pve outdoor boxes for a clean look.
Regardless of the conduit material, I will end up running 12/2 romex to the box(es) with no THHN involved.
#12
Member
Join Date: Jul 2014
Location: usa
Posts: 258
Upvotes: 0
Received 0 Upvotes
on
0 Posts
So I can run 2 lengths of 12/2 romex down a single piece of 1" EMT and not need to worry about heat buildup or whatever? I just want to be sure. Thanks.
The message you have entered is too short. Please lengthen your message to at least 25 characters.
#13
It's for running a chest freezer and a refrigerator, each requiring a 20A circuit.
Also, is this what you're talking about (for a CH style box)? - Eaton Type Ch 20 Amp Combination Arc Fault Circuit Breaker
#14
Member
Thread Starter
Join Date: Aug 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I agree with installing 20 amp circuits for both appliances, but you still do not need more than 15 amp GFCI receptacles.
That would be correct if you have the tan colored CH series Cutler-Hammer panel. If you have the gray colored BR series Cutler-Hammer box you'll need a different breaker. Check with your local AHJ to see if they'll require you to use the AFCI breaker and also ask if the GFCI receptacles need to be tamper resistant.
#15
The code allows for 15 amp slot devices to be used if there is more than one place to plug into the circuit. A standard duplex is two.
Last edited by pcboss; 08-10-14 at 06:42 AM.
#16
Member
Join Date: Jul 2014
Location: usa
Posts: 258
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Okay. Can you expand on that at all? Is that simply because an appliance that actually required 20A would have a plug with one of the slots sideways, so these appliances (which do not have a 20A plug configuration) wouldn't require a 20A receptacle but a 20A circuit breaker would be warranted in case of spikes when the compressor kicks on?
AND you may install a 20 amp GFCI receptacle outlet on a 12 gauge,20 amp protected circuit if you wish to.
#17
AND you may install a 20 amp GFCI receptacle outlet on a 12 gauge,20 amp protected circuit if you wish to.
#19
Member
Thread Starter
Join Date: Aug 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The wall that I plan on running the wire down is a cinder block wall with ground (dirt in this case) on the other side. Does that constitute a "wet location" and would I need to adjust my setup accordingly? What would that entail?
Please advise. Thanks.
Please advise. Thanks.
Last edited by brshoemak; 08-10-14 at 12:02 PM.
#22
Member
Thread Starter
Join Date: Aug 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok, I'm back. Went to Lowes picked up a shload of supplies. I'm going to do AFCI --> romex --> junction box --> THHN (with wire nuts) --> 2-gang box with 2 GCI (everything 12AWG and 20A gear). There will be two pieces of romex entering the junction box and 6 strands of THHN leaving the box.
First off, holy crap are AFCI breakers expensive! Now, on to my question:
In the junction box where I'm going to convert the romex to THHN, the rear of the box has a location for a ground screw.
How should I handle grounding? Am I correct in assuming I can just wrap a separate piece of 12AWG THHN wire around that screw, then twist and wirenut that piece along with the grounds the romex and THHN - for one circuit? Then would I do the same for the other circuit - so only two pieces of 12AWG wire would be wrapped around the ground screw, one for each circuit?
Also, since the metal junction box will be the ground point for all the connected metal conduit/boxes, I don't need to worry about adding a ground point to the box where the receptacles will be correct? Obviously the receptacles themselves would be grounded.
btw, if seemingly everything residential requires a AFCI nowadays (with the latest NEC), why are there so few AFCI breakers on the shelves, but boxes upon boxes of 'normal' circuit breakers remain? Am I safe to assume that commercial work does not require AFCI in most cases?
First off, holy crap are AFCI breakers expensive! Now, on to my question:
In the junction box where I'm going to convert the romex to THHN, the rear of the box has a location for a ground screw.
How should I handle grounding? Am I correct in assuming I can just wrap a separate piece of 12AWG THHN wire around that screw, then twist and wirenut that piece along with the grounds the romex and THHN - for one circuit? Then would I do the same for the other circuit - so only two pieces of 12AWG wire would be wrapped around the ground screw, one for each circuit?
Also, since the metal junction box will be the ground point for all the connected metal conduit/boxes, I don't need to worry about adding a ground point to the box where the receptacles will be correct? Obviously the receptacles themselves would be grounded.
btw, if seemingly everything residential requires a AFCI nowadays (with the latest NEC), why are there so few AFCI breakers on the shelves, but boxes upon boxes of 'normal' circuit breakers remain? Am I safe to assume that commercial work does not require AFCI in most cases?
#23
Am I correct in assuming I can just wrap a separate piece of 12AWG THHN wire around that screw, then twist and wirenut that piece along with the grounds the romex and THHN - for one circuit? Then would I do the same for the other circuit - so only two pieces of 12AWG wire would be wrapped around the ground screw, one for each circuit?
if seemingly everything residential requires a AFCI nowadays (with the latest NEC), why are there so few AFCI breakers on the shelves, but boxes upon boxes of 'normal' circuit breakers remain? Am I safe to assume that commercial work does not require AFCI in most cases?
#24
Member
Thread Starter
Join Date: Aug 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the information - makes sense. Now I just need to be able to figure out how to successfully pretwist the 5 grounds so they'll be secure in the wire.
Now, in terms of running romex, am I correct that you can't bundle two cables under a single staple and instead need to run them side-by-side?
Also, usually I see romex ran along joists, but is there any limitation in running it along the perpendicular wood beam that supports the joists? Will hammering romex staples into it cause any problem to the joists?
Now, in terms of running romex, am I correct that you can't bundle two cables under a single staple and instead need to run them side-by-side?
Also, usually I see romex ran along joists, but is there any limitation in running it along the perpendicular wood beam that supports the joists? Will hammering romex staples into it cause any problem to the joists?
#25
makes sense. Now I just need to be able to figure out how to successfully pretwist the 5 grounds so they'll be secure in the wire.
is there any limitation in running it along the perpendicular wood beam that supports the joists? Will hammering romex staples into it cause any problem to the joists?
#26
makes sense. Now I just need to be able to figure out how to successfully pretwist the 5 grounds so they'll be secure in the wire.
is there any limitation in running it along the perpendicular wood beam that supports the joists? Will hammering romex staples into it cause any problem to the joists?
#27
Member
Join Date: Jul 2014
Location: usa
Posts: 258
Upvotes: 0
Received 0 Upvotes
on
0 Posts
#28
Member
Thread Starter
Join Date: Aug 2014
Location: USA
Posts: 26
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Basic Electrical Skills :: How to Install a Wire Nut
Read the instructions on the wire not box, pre-twisting is not necessarily a requirement.
#29
I'd be wary of trying to do that with 5 #12 wires and being sure they were all making contact inside the wire nut instead of having some being pushed out.
#30
Member
Join Date: Jul 2014
Location: usa
Posts: 258
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'm saying that it's just a tad bit more difficult to twist together 5 #12 wires vs 2.
where are you twisting 5 grounds
run the 2 cables all the way to the outlets.............if you use EMT place a connector with a bushing at the top.
My understanding is that I need to (or should) convert the romex to THHN before it enters the EMT.