How do I make my switched outlet hot 24/7
Old 08-17-14, 09:32 AM
E
My outlet is connected to a switch that is in the same box as my switch to my porch light so I'm assuming they're connected together somehow. I want to add recessed lighting that is controlled by that switch that control the outlet. So how do I keep that outlet on while I make my switch be able to switch my lights.
Old 08-17-14, 09:38 AM
ray2047's Avatar
We need to know the wiring at the receptacle and if both plug-ins are switched or if only half of the receptacle is switched.
At the switch box do you have a group of whites connected only to each other (usually in back)? At the switch that controls the receptacle is there a red wire connected to it?
Old 08-17-14, 10:17 AM
pcboss's Avatar
Received 194 Upvotes on 170 Posts
The circuit needs to be grounded and also have capacity to add the new lighting load. What else is on the circuit?
Old 08-17-14, 06:23 PM
does the switch say off and on..........great......you have a single pole switch.
remove the single pole switch from the box.
the single pole switch will have 2 brass screws with a wire on each screw.
remove both wires and wirenut them together with a pigtail.
this pigtail will be the new hot feed for your switch.
and your outlet will stay on.
Old 08-17-14, 10:43 PM
Received 3,973 Upvotes on 3,566 Posts
John.... what if the switch is connected with a switch loop ?
Connecting the wires will keep the receptacle on but what about neutral ?
Old 08-18-14, 05:20 AM
PJmax
PJmax is offline Forum Topic Moderator
PJmax is right!!
i left you hanging with a hot pigtail on one side of a single pole switch.
but as PJmax says...you must have a neutral(white) wire.
so look deep into your switch box...................
you are looking for a wirenut with 2 or 3 white wires
if you find it....you have your neutral wire for the new lighr fixture.
attach the white here for the new light.
attach the black wire to the other screw on the single pole switch.
if you do not find it in your switch box you will have to get your neutral from the porch light fixture box.
Old 08-19-14, 06:37 PM
E
Here's what it is
So my neutrals and my grounds are nutted together. My hot from the left side is connected to the porch light switch. A red wire is connected to that switch as well. The hot from the right side is nutted together with that red wire and a black wire is connected in there to the bottom of the outlet switch. A red wire is connected to the outlet switch and runs out of the box.
Old 08-19-14, 06:42 PM
E
In the outlet. One red is connected to the right side. Two neutrals are connected to the left side. My grounds are grounded and my black hots are nutted together
Old 08-19-14, 06:53 PM
ray2047's Avatar
At the receptacle:
  • Remove the red wire and cap with a wire nut.
  • Connect a pigtail to the black wires and connect to the brass side of receptacle.
  • All other wires remain as connected.
At the switch:
  • Disconnect the red from the receptacle switch and cap with a wire nut.
  • Connect the black of the cable to the new lights to where you disconnected the red..
  • Connect the white of the new light cable to the other whites.
  • All other connections remain the same.
Old 08-19-14, 07:03 PM
E
So I'll have 3 romex's in the switch box? Is there one of those diagrams you could draw?
Old 08-19-14, 07:59 PM
ray2047's Avatar
Give me a bit. Do you just need the switch?
Old 08-19-14, 08:50 PM
ray2047's Avatar
Old 08-20-14, 06:09 AM
E
Ok thanks a lot. I'll get that wired up and it should work fine. The switch is on an outside wall so are there any restrictions I should be aware of before going in the attic?
Old 08-20-14, 06:21 AM
ray2047's Avatar
No restrictions I know of. Best way to fish the cable will be to remove the box to give you an opening and then replace with an old work box. If the wall is insulated you may need to use a fish tape.
Old 08-21-14, 03:39 PM
E
From the attic to the wall, is there like a 2x4 covering the top of the wall opening or is it just filled with insulation or do you know?
Old 08-21-14, 04:41 PM
ray2047's Avatar
There would be a double top stud plate. There is probably a hole where at least one other cable goes into the wall. It may be large enough for your new cable.
Old 08-21-14, 06:15 PM
pcboss's Avatar
Interior walls are not typically insulated.
Old 08-23-14, 09:46 PM
E
The wall on an outside wall
This is an exterior wall so there may be insulation.
Old 08-23-14, 09:56 PM
ray2047's Avatar
So you may need to force a fish tape through the insulation.