Sizing conductors for spa hook-up
#1
Member
Thread Starter
Join Date: Oct 2012
Location: USA
Posts: 15
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Sizing conductors for spa hook-up
The manual for an outdoor spa specifies a 50 amp main breaker and #8-3 wire to run to the subpanel (up to 100')
My question is, the spa is 210' away from the main panel. Is there enough safety factor allowed using 8 gauge wire, or should it be larger (#6 ga?)
Is the 50 amp breaker OK in either case?
Thanks everyone.
My question is, the spa is 210' away from the main panel. Is there enough safety factor allowed using 8 gauge wire, or should it be larger (#6 ga?)
Is the 50 amp breaker OK in either case?
Thanks everyone.
#2
The 8-3 if NM is only good for 40 amps. You need at least #6. Once outside the house the ground will need to be insulated.