The manual for an outdoor spa specifies a 50 amp main breaker and #8-3 wire to run to the subpanel (up to 100')
My question is, the spa is 210' away from the main panel. Is there enough safety factor allowed using 8 gauge wire, or should it be larger (#6 ga?)
Is the 50 amp breaker OK in either case?
Thanks everyone.
 
Sponsored Links
  #2  
Old 08-19-14, 05:55 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,352
The 8-3 if NM is only good for 40 amps. You need at least #6. Once outside the house the ground will need to be insulated.
 
  #3  
Old 08-20-14, 06:36 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,212
My question is, the spa is 210' away from the main panel.
How much of that is outside the house?
 
  #4  
Old 08-20-14, 06:43 AM
Member
Join Date: Jul 2014
Location: usa
Posts: 279
run a 4 wire ,#4 gauge feed to a sub panel by the spa

you might use the 100 amp al trailer service from lowes.
 