Splicing a 240V Pool Circuit
#1
Member
Thread Starter
Join Date: Aug 2014
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Splicing a 240V Pool Circuit
I am relocating my main panel 20 ft. The existing 40A 240VAC pool circuit is a home run from existing panel to pump (4 individual conductors). Would like to cut line in garage and install junction box, then splice in a new 20ft. Length of wire to the new panel. Is this within code?? I am from Long Island, NY. Contractor is telling me a pool feed has to be a home run. Thanks
#2
As long as the junction is permanently accessible it would meet the NEC requirements. Your local area may have an amendment to the NEC. You should be able to ask your local building authority.
#3
Member
Thread Starter
Join Date: Aug 2014
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Pcboss, thanks for the response. Electrician said it had to be home run because of ground wire. Ground has to be straight run to pool pump and cannot be spliced. Any thoughts on this??
#9
The GEC from the panel to the first electrode must be one continuous piece or irreversibly splice. That has nothing to due with the EGC for the pool.
#10
PCBoss I think Swidster ask about the GEC because of my off hand remark in post #6 suggesting the contractor might be con fusing rules for GED with rules for EGC. Didn't mean to confuse things.
#11
Member
Thread Starter
Join Date: Aug 2014
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks guys. You may have saved me $1500 that they wanted to charge me to run a new line from new panel to pool pump. I had said why not just splice in a junction box in garage, but they started with the "must be a straight run from panel to pump! hope this flys!!
#12
must be a straight run from panel to pump!
The NEC does not require equipment grounding wires to be continuous. Your location might be different, a call to the AHJ might be in order.
#15
Member
Thread Starter
Join Date: Aug 2014
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Guys, no good, electrician says inspector will not allow a splice in line from pool pump to panel. I also called local electric supply and they said the same thing - although they thought the requirement was rediculous and said to do it anyway. But my electrician said he would not install anything against code. In addition he said that the inspectors are extra sensitive to pool wiring! Thanks any way. Now he is proposing a sub panel instead of running a new line, we'll see if it's cheaper then the $1500 for a new line😳😁. Swidster
#16
Member
Thread Starter
Join Date: Aug 2014
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Guys, electrician said it's no good! Inspector will not allow a splice in pool pump circuit. I spoke to a local electrical supply guy also and he confirmed the same, although he thought it was an unnecessary requirement. He said I should splice anyway, but I told him I was having other work done and then he sided with the electrician. Now my electrician has suggested a sub panel, so the pool pump ckt will remain and avoid running 100+ ft of me pool feed. We'll se what that costs!!😳😳