Split wiring short circuit
#1
Split wiring short circuit
I am replacing an old receptacle with a new one and I thought I had wired everything up in the correct way but this immediately tripped the panel breaker. https://docs.google.com/file/d/0BwSN...p=docslist_api
#2
You have a multi wire circuit. You need to break out the little tab between the two brass screws to separate the black and red wires of the three wire cable (top right). Look closely at the old device and you will see the missing tab between the two brass screws.
As a note: You should not put two wires under one screw. The black and red marked "top" should be connected together with a pigtail, and the pigtail should then be connected to the receptacle screw.
As a note: You should not put two wires under one screw. The black and red marked "top" should be connected together with a pigtail, and the pigtail should then be connected to the receptacle screw.
#3
You will have to remove the bridging clip on the black/red side of the receptacle. Splice the black and red wire at the top together so that only one wire connects at the receptacle.



#6
I don't know if you ever noticed it or used it, but this type of wiring is designed to have one half of a receptacle always hot, and one half of the outlet switched.
This is required by code in living spaces that don't have a ceiling light.
It's designed to where you can turn on a lamp upon entering room.
This is required by code in living spaces that don't have a ceiling light.
It's designed to where you can turn on a lamp upon entering room.
#7
Actually in this case there are two circuits to that receptacle. That's the reason for the breaker tripping. This was common in kitchens. Now with GFI receptacles the two circuits would have to go to two GFI receptacles.
#8
That's the reason for the breaker tripping
Sorry for the post, school me. I've seen multi-wire circuits, but never one that provided power to upper and lower halves of receptacle separately.
The only thing I can think of is Dishwasher/Disposal switched combo

#9
The red wire is one circuit and the black wire is the other circuit.
The neutral is shared. So if you were to use a voltmeter at the receptacle and you checked between the two smaller slots.... you'd measure 240vac.
The neutral is shared. So if you were to use a voltmeter at the receptacle and you checked between the two smaller slots.... you'd measure 240vac.
#10
In Canada it is/was (not sure if it still is) required to have the kitchen counter top receptacles split wired in this manner. The OP is non-US and could be from Canada.
#11
Is this the same receptacle you were trying to replace in http://www.doityourself.com/forum/el...ng-wiring.html
#15
That circuit seems to be an outlet on the counter top and the dishwasher. There is another outlet nearby with 3wires, 1 black 1 red (tab removed) 1 white. Is that split also?
Might be expensive if I need 2 separate gfci breakers at the panel.
Might be expensive if I need 2 separate gfci breakers at the panel.
#20
I pulled the dishwasher out this weekend and it turns out the same circuit as the outlet is connected to the dishwasher.
It was hard wired with the electrical box just dangling on the floor (which given that the supply pipe was leaking is worrying).
I'm going to attach the electrical box to the backboard and wire in a receptacle and a plug for the dishwasher.
However, I understand that under the CEC, these split wire circuits with dishwashers now need AFCI and GFCI combined?
It was hard wired with the electrical box just dangling on the floor (which given that the supply pipe was leaking is worrying).
I'm going to attach the electrical box to the backboard and wire in a receptacle and a plug for the dishwasher.
However, I understand that under the CEC, these split wire circuits with dishwashers now need AFCI and GFCI combined?
#21
I understand that under the CEC, these split wire circuits with dishwashers now need AFCI and GFCI combined?
#23
CJ, it that Class A 5 MA protection or the Class B 30 MA protection?
The 2014 National Electric Code now requires both Combination Arc Fault
and Ground Fault protection on all 1-Pole, 15 A, and 20 A kitchen and laundry
circuits. Prior to the release of the Dual Function Circuit Breaker, a contractor
or homeowner’s only choice was to use a Combination Arc Fault circuit breaker
in conjunction with an expensive, bulky Ground Fault receptacle. The new Dual
Function circuit breakers help reduce cost and eliminate the hassle of using
two separate devices to provide essential protection.
and Ground Fault protection on all 1-Pole, 15 A, and 20 A kitchen and laundry
circuits. Prior to the release of the Dual Function Circuit Breaker, a contractor
or homeowner’s only choice was to use a Combination Arc Fault circuit breaker
in conjunction with an expensive, bulky Ground Fault receptacle. The new Dual
Function circuit breakers help reduce cost and eliminate the hassle of using
two separate devices to provide essential protection.
I suspect it won't be long till all manufacturers have a similar breaker with the dual function.