Replacing Westinghouse breakers
#1
Member
Thread Starter
Join Date: Sep 2014
Posts: 2
Received 0 Votes
on
0 Posts
Replacing Westinghouse breakers
Greetings
There are four 15 Amps split duplex receptacles close enough to the kitchen sink to require GFCI protection I would like to replace the existing breakers with GFCI breakers The panel is Westinghouse WB1216 and the breakers are DNPL 15 15 940117 I did a search looking for replacements but came up empty
I would appreciate some info as to finding the correct breaker
Thank you
There are four 15 Amps split duplex receptacles close enough to the kitchen sink to require GFCI protection I would like to replace the existing breakers with GFCI breakers The panel is Westinghouse WB1216 and the breakers are DNPL 15 15 940117 I did a search looking for replacements but came up empty
I would appreciate some info as to finding the correct breaker
Thank you
#2
Welcome to the forums!
Eaton/Cuttler Hammer type BR breakers are replacements for Westinghouse panels.
Here is one example: Shop Eaton Type BR 20-Amp Ground Fault Circuit Breaker at Lowes.com
Eaton/Cuttler Hammer type BR breakers are replacements for Westinghouse panels.
Here is one example: Shop Eaton Type BR 20-Amp Ground Fault Circuit Breaker at Lowes.com
#6
The OP is in Canada and referring to kitchen counter top receptacles. Canada code requires (or required) a duplex receptacle to be split wired (top and bottom separated) with two circuits.
#7
Member
Thread Starter
Join Date: Sep 2014
Posts: 2
Received 0 Votes
on
0 Posts

Thank you for welcome and replies
this breakers are expensive
Geochurchi asked
'' What do you mean by split circuits?''
My post said split receptacles [fed by 3 wire circuits or multiwire circuits]
The house was built in the early 90s and apparently at that time the Provincial Code did not required GFCI protection for the kitchen counter receptacles however it was required for bathrooms
Regards
DL


Geochurchi asked
'' What do you mean by split circuits?''
My post said split receptacles [fed by 3 wire circuits or multiwire circuits]
The house was built in the early 90s and apparently at that time the Provincial Code did not required GFCI protection for the kitchen counter receptacles however it was required for bathrooms
Regards
DL
#8
My post said split receptacles [fed by 3 wire circuits or multiwire circuits]