Replacing Westinghouse breakers

Greetings

There are four 15 Amps split duplex receptacles close enough to the kitchen sink to require GFCI protection I would like to replace the existing breakers with GFCI breakers The panel is Westinghouse WB1216 and the breakers are DNPL 15 15 940117 I did a search looking for replacements but came up empty
I would appreciate some info as to finding the correct breaker
Thank you
 
  #2  
Old 09-04-14, 02:55 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,802
Received 252 Votes on 220 Posts
Welcome to the forums!

Eaton/Cuttler Hammer type BR breakers are replacements for Westinghouse panels.

Here is one example: Shop Eaton Type BR 20-Amp Ground Fault Circuit Breaker at Lowes.com
 
  #3  
Old 09-04-14, 04:53 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Location: United States
Posts: 4,963
Received 88 Votes on 83 Posts
What do you mean by split circuits? If it is a Multi wire circuit the GFCI protection will work. i.e. Shared neutral.
Geo
 
  #4  
Old 09-04-14, 05:06 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,541
Received 0 Votes on 0 Posts
I too wonder what you mean by split circuit. Do you mean like a multiwire circuit (With a common neutral) or tandem breakers(2 breakers that take the space of 1)?
 
  #5  
Old 09-04-14, 06:45 PM
W
Member
Join Date: Feb 2014
Posts: 31
Received 0 Votes on 0 Posts
I had the same problem with my old Westinghouse panel I solved the problem by using one 15 amp GFCI receptacle and daisy chaining it to the other 3 receptacles for protection.
 
  #6  
Old 09-04-14, 06:52 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,802
Received 252 Votes on 220 Posts
The OP is in Canada and referring to kitchen counter top receptacles. Canada code requires (or required) a duplex receptacle to be split wired (top and bottom separated) with two circuits.
 
  #7  
Old 09-04-14, 07:06 PM
D
Member
Thread Starter
Join Date: Sep 2014
Posts: 2
Received 0 Votes on 0 Posts
Smile

Thank you for welcome and replies this breakers are expensive

Geochurchi asked

'' What do you mean by split circuits?''

My post said split receptacles [fed by 3 wire circuits or multiwire circuits]

The house was built in the early 90s and apparently at that time the Provincial Code did not required GFCI protection for the kitchen counter receptacles however it was required for bathrooms
Regards
DL
 
  #8  
Old 09-04-14, 07:26 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,758
Received 97 Votes on 87 Posts
My post said split receptacles [fed by 3 wire circuits or multiwire circuits]
Since you have a shared neutral in the 3-wire multiwire branch circuits, you'll need a 2 pole GFCI breaker.
 
 