Water Wells, Pumps and Generators!
Hello guys!
I have a 1000ft well, pump is at 550ft. I am running a 3hp-10gpm-230V-Jacuzzi pump. Full load amp 17.1, the well is 200 feet from the elect service.
I know the pump start up will be more than 17.1 so what size generator can I pick up that will handle it comfortably?
I think a 5000 would do it but I would like your input please. I could be way off.
Thanks everyone!
Robert
I have a 1000ft well, pump is at 550ft. I am running a 3hp-10gpm-230V-Jacuzzi pump. Full load amp 17.1, the well is 200 feet from the elect service.
I know the pump start up will be more than 17.1 so what size generator can I pick up that will handle it comfortably?
I think a 5000 would do it but I would like your input please. I could be way off.
Thanks everyone!
Robert
#2
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes
on
30 Posts
I could be way off.
There is also the problem of rotational mass of the generator itself. I wouldn't be surprised that attempting to start that pump put such a heavy load on the generator as to cause it to stall the engine.
What I would do is to get a clamp-on ammeter and measure the actual starting amperage of the pump motor and time the duration until the amperage drops to the normal running amperage of about 17 amperes. You then need a generator with a surge capacity equal to or more than the pump starting surge. Even then I would want to try the generator before committing to buying it to be certain it will do the job.
#3
Member
Join Date: Aug 2014
Location: U.S.A.
Posts: 58
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I have no experience with this information nor its accuracy.
Guidelines for using generators with submersible well pumps
Guidelines for using generators with submersible well pumps
#7
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks guys!
I will look into it more and run test. Not sure of the LRA that was not on the information I was provided. I have had the pump out one time to replace some pipe but did not look at it that well.
I will keep you posted.
Thanks again.
Robert
I will look into it more and run test. Not sure of the LRA that was not on the information I was provided. I have had the pump out one time to replace some pipe but did not look at it that well.
I will keep you posted.
Thanks again.
Robert
#8
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
OK guys here it is the start amps are 29 to 30. The motor only pulls this for less than 1 second and drops to 14 to 15 for run amps.
Thanks guys all help is appreciated. Have a great day!
Thanks guys all help is appreciated. Have a great day!
#13
As you mentioned the 30amp draw at start up only lasts 1-2 seconds then drops down to 14-15 amps. That is 3600 watts.
If you plan to run other things other then the well, then maybe a 10KVA generator might be in order. Otherwise I would think a 7500 watt would do you fine.
If you plan to run other things other then the well, then maybe a 10KVA generator might be in order. Otherwise I would think a 7500 watt would do you fine.
#14
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks! I am looking at a 10 KVA and decided that was the way to go thanks to you guys (I would like to have a little more power than I need). I will only be using it in a small amount but the only time it will get hit hard is when the pump comes on and we don't use much water and I have a huge accumulator and a 300 gal tank for spare water.
We are trying to be more self sufficient out here on the plains with a wood burning stove and enough food and supplies to go months without service the water was the only issue due to the well depth. I can pump up 300 to 600 gal for storage in no time and shut the unit down and not need power for long periods of time.
I am also going to go with a propane gen because we have a 1000 gal propane tank that stays over 1/2 to 3/4 full all the time so that will give me a a gal per hr at 1/2 power....I think that's the way I added it up.
Getting as prepared as I can to be off the grid if the time comes.
Thanks everyone!
We are trying to be more self sufficient out here on the plains with a wood burning stove and enough food and supplies to go months without service the water was the only issue due to the well depth. I can pump up 300 to 600 gal for storage in no time and shut the unit down and not need power for long periods of time.
I am also going to go with a propane gen because we have a 1000 gal propane tank that stays over 1/2 to 3/4 full all the time so that will give me a a gal per hr at 1/2 power....I think that's the way I added it up.