2-2-2-4 Aluminum SER Service Entrance Cable

Reply

  #1  
Old 09-09-14, 08:13 AM
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 11
2-2-2-4 Aluminum SER Service Entrance Cable

2-2-2-4 Aluminum SER Service Entrance Cable .....
Can I use this cable for dedicated 30 amp 175' run from my home service panel to an RV?
 
Sponsored Links
  #2  
Old 09-09-14, 09:53 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,213
Maybe although it would be overkill and a waste. What is the voltage you need; 120 volt, 240 volt or 120/240 volt. How were you planning on installing the cable? SER cable needs to be supported and isn't intended for direct burial or aerial applications.
 
  #3  
Old 09-09-14, 10:43 AM
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 11
Only need 120 volt....I may go with a 50 amp breaker. My current RV takes 30 amp. Option of using this cable in conduit? Just looking for cheapest way to make a run of 175', 80 feet inside/ basement, and about 100' outside buried in conduit.
 
  #4  
Old 09-09-14, 10:46 AM
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 11
I could put in 2 pole 50 amp for future 120/240 use.
 
  #5  
Old 09-09-14, 12:39 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,361
SER cannot be used underground, even if in conduit.
 
  #6  
Old 09-09-14, 05:15 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,213
I may go with a 50 amp breaker. My current RV takes 30 amp.
If the RV receptacle is rated at 30 amps, the breaker cannot exceed 30 amps. You cannot use a 50 amp 2 pole breaker without setting up a subpanel and feeding the RV receptacle with a 30 amp single pole breaker from the subpanel.
 
  #7  
Old 09-10-14, 07:16 AM
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 11
Yeah. I am going to do a 30 amp now...a 50 if I get a different RV down the road. Just planning on what type of wire. May have to go with a UF 6/3...although more expensive. Just seeing if there are direct cheaper options. Maybe SEC inside and direct bury or type that can conduit outside. Big price difference between 6 gauge UF and SEC.
 
  #8  
Old 09-10-14, 07:23 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,361
Individual conductors are much easier to pull in conduit than a cable.
 
  #9  
Old 09-10-14, 07:38 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,213
Individual conductors are much easier to pull in conduit than a cable.
And individual conductors should be cheaper than a 6-3 UF Cable too.
 
  #10  
Old 09-10-14, 07:43 AM
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 11
Is SER 2-2-2-4 inside ok then junction to....
" Southwire’s Quadruplex URD used for secondary distribution and underground service. It can be used for direct burial or in ducts." ....2-2-2-4
from Homedepot for outside. A lot cheaper than a 6/3 UF route. Will a 2 gauge fit into a square d breaker direct? or just put into sub-panel first?
 
  #11  
Old 09-10-14, 07:49 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,361
You are going to need a panel at the studio and a grounding system.
 
  #12  
Old 09-10-14, 07:49 AM
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 11
liking the Single conductor idea...could go with 4 or 6 gauge?....would you pull 4 wires for future 50 amp 120v...or get away with 3 and use neutral as the ground?
 
  #13  
Old 09-10-14, 07:50 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,213
Is SER 2-2-2-4 inside ok then junction to....
" Southwire’s Quadruplex URD used for secondary distribution and underground service. It can be used for direct burial or in ducts." ....2-2-2-4
from Homedepot for outside.
That would work. The junction box will have to be a NEMA 3R raintight.

Will a 2 gauge fit into a square d breaker direct? or just put into sub-panel first?
Probably not. You may have to splice to a smaller wire size at each end.
 
  #14  
Old 09-10-14, 07:50 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,361
You need 4 wires to a sub panel.
 
  #15  
Old 09-10-14, 07:53 AM
Member
Thread Starter
Join Date: Jan 2014
Location: USA
Posts: 11
I'm thinking about a 50amp breaker in my main panel...then running single pole wires.. then a 30 amp breaker at sub panel to plug. In future can just replace 30 with 50 or wire direct to the plug.
 
  #16  
Old 09-10-14, 11:11 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
Run 2-2-2-4 SER on 60A breaker from inside panel to outside junction box.

Transition from SER to URD in outside junction box.

Run URD sleeved in 1.5'' conduit until 24'' underground.

Direct bury URD until coming up inside conduit into panel.

Install 6 or 8 circuit outdoor panel OR a RV pedestal.


Example of pedestal: GE RV Lighted Earth Buried Pedastal 100A 120/240V Unmetered with 50 Amp, 30 Amp, 20 Amp GCFI Circuit Protected Receptacles-GE1LU532ESL at The Home Depot
 