Using 6/3 in place of 6/2 Question


  #1  
Old 09-09-14, 07:29 PM
F
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Using 6/3 in place of 6/2 Question

I am running a 40 foot run of 6/3 wire for a 240v 50 amp max welder. Using a 60 amp breaker in my 200 amp box in my house. Entire run is indoors. My question is this:

I ran 6/3 to future proof my run if I decide to add a subpanel in the garage instead of just the outlet. Because of this I will have an unused wire in the romex jacket. What is the proper way to make the unused wire legal? (put in box or out of box, cap with wire nut, etc).

Also is there a recommendation on using certain color wires, white / black I am assuming is the standard. Also should I use the 8 gauge ground wire for the ground, or switch to the unused 6 gauge wires as the ground?

Thank you.
 
  #2  
Old 09-09-14, 08:05 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,935
Received 181 Upvotes on 159 Posts
For a 240 volt welder use the black and the red and the bare or green. Cap the white in the box for future use.
 
  #3  
Old 09-10-14, 07:35 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,841
Received 178 Upvotes on 161 Posts
Also should I use the 8 gauge ground wire for the ground, or switch to the unused 6 gauge wires as the ground?
6-3 NM B cable (aka romex) has a #10 grounding conductor.
 
  #4  
Old 09-10-14, 05:56 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,452
Upvotes: 0
Received 266 Upvotes on 242 Posts
Use the green or bare wire in the cable for the ground (equipment grounding conductor).

In the U.S. it is actually mandatory for EGCs to be bare or green, and neutrals (grounded conductors) to be white or light gray. (For wires #4 or larger, black wires with the correct color tape at both ends are permitted.)

For wire sizes 8 and larger the EGC may be thinner than the current carrying conductors hence the #10 EGC in the case above.

For futureproofing, I would run #4 gauge wires (#8 EGC). Using #6 wire, everything else (perhaps including an air conditioner?) fed by the subpanel can be using at most 10 amps @240 volts or 20 amps @120 volts before you use the welder.
 

Last edited by AllanJ; 09-10-14 at 06:25 PM.
 