Replaced 15 Amp Breakers and still no power in 1/2 of house.

Replaced 15 Amp Breakers and still no power in 1/2 of house.

Reply

  #1  
Old 09-10-14, 08:13 AM
E
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Replaced 15 Amp Breakers and still no power in 1/2 of house.

Name:  image.jpg
Views: 2427
Size:  46.2 KBName:  breaker box 2.jpg
Views: 2014
Size:  44.9 KBI have a 1,000 sq. ft. rental property. Turned on an air conditioner window unit, it immediately turned off within a few seconds. I go to check the breaker that typically flips and found it was still in the ON position. I flipped the breaker and nothing happened. The power is still out on that one half of the house. I replaced both of the 15 Amp breakers that I thought were faulty but to no avail the power is still out. I am not a licensed electrician but am educated enough in regards to electricity and installing new outlets and other miscellaneous stuff throughout my property. I am at a lost here. Looking for an easy explanation of what I should do next? Maybe pay to have an electrician come and check it out? I am on a very tight budget. Thank you community I appreciate your feedback.
 
  #2  
Old 09-10-14, 08:36 AM
lawrosa's Avatar
Super Moderator
Join Date: Dec 2010
Location: Galivants Ferry SC USA
Posts: 18,152
Received 62 Votes on 54 Posts
Welcome to the forums..............

Stand by for one of the pros to assist... It would seem you lost one leg to the home... Possibly the main breaker at fault? IDK..

Please be very careful working in the panel... You can be killed.... If you are unsure then yes a pro should be called in..

I assume a test with a multimeter can confirm a few things. Do you have one and know how to use it?
 
  #3  
Old 09-10-14, 08:40 AM
E
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
I do have a multi-meter and have a general idea of how to use it. Maybe I am missing something here. Would the MAIN breaker be located outside of my home? Versus the MAIN at the top of my breaker panel?
 
  #4  
Old 09-10-14, 08:46 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,758
Received 97 Votes on 87 Posts
Since the breakers are adjacent, it is not likely you lost a leg into the house, but I would start at the main lugs anyway. What is the voltage across the 2 main lugs? It should be near 240 volts. Next, check the lug on each of the two 15 amp breakers to neutral, they should read around 120 volts. If these two tests check out you have a problem within the two circuits. It doesn't appear these are multiwre branch circuits because each hot conductor is black, but it wouldn't hurt to check to see if each circuit has it's own dedicated white neutral conductor.
 
  #5  
Old 09-10-14, 08:47 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,222
Received 103 Votes on 89 Posts
It looks like this is your service panel.

Check between both incoming legs to ground and see if you get 120 volts and 240 volts between hot to hot. Report back.
 
  #6  
Old 09-10-14, 10:17 AM
Gunguy45's Avatar
Super Moderator
Join Date: Dec 2007
Location: USA
Posts: 21,113
Received 3 Votes on 3 Posts
You said rental property...I'm assuming you are the owner?
 
  #7  
Old 09-10-14, 10:19 AM
E
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Yes I am the owner of this property...
 
  #8  
Old 09-11-14, 08:36 AM
E
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Everything in Panel tested okay.

Ends up DTE energy replaced the old analog meters outside with new digital meters the day before I had this issue. I didn't even notice! Everything in the panel tested good. Now I will have to deal with having a house with only 1/2 power. With 33,000 people with no power in the area, I'm grateful to even have half power. DTE has to come out and replace the fuses in the meters.
 
  #9  
Old 09-11-14, 09:39 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
Never heard of fuses in meters. Just the Kearneys on the pole.
 
  #10  
Old 09-11-14, 07:51 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,758
Received 97 Votes on 87 Posts
Everything in the panel tested good.
If everything in the panel tested good, you have no utility company or meter issues and can proceed to troubleshoot and repair your problem. It's time to take a hard look at those two circuits.

DTE has to come out and replace the fuses in the meters.
Why? You have full power to your panel.
 
 