Recesed Lights On 3-way Switches


  #1  
Old 09-13-14, 11:25 AM
B
Member
Thread Starter
Join Date: May 2014
Location: USA
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Recesed Lights On 3-way Switches

Linesman, When I saw your 4 lights diagram between 2 three-way switches, I figured it was the solution to my problem. I finally found an outfit that sold 12-4 with ground (spent the big bucks for the wire) and installed my four recessed lights as you indicated. All the colors seemed quite dummy-proof! Despite triple-checking every single connection, it blows the circuit breaker every time! I even tried another breaker. Your diagram makes sense as a series of parallel circuits, but I can't get it to work. Help!!

Separated from: http://www.doityourself.com/forum/el...le-lights.html. Diagram referenced below.
Name:  SC78.jpg
Views: 4441
Size:  35.3 KB
 

Last edited by ray2047; 09-13-14 at 11:45 AM.
  #2  
Old 09-13-14, 11:48 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,575
Upvotes: 0
Received 15 Upvotes on 13 Posts
Linesman hasn't posted in over two years but if you will tell us exactly what you have and how you wired it we will help.
 
  #3  
Old 09-13-14, 11:49 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 71,652
Received 3,328 Upvotes on 2,987 Posts
Welcome to the forums.

The diagram is correct and will work. It would be pretty hard for us to double check your wiring.

That method of wiring a lighting system is not ideal. It was a special purpose application.
 
  #4  
Old 09-13-14, 07:40 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 11,208
Received 172 Upvotes on 155 Posts
There is an issue with the diagram if your AHJ has adopte the 2011 NEC. The second 3-way switch box must have a neutral conductor that this diagram doesn't have. You could have spared yourself the cost of the 12-4 NM B cable had you come here first.
 
  #5  
Old 09-13-14, 07:58 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 71,652
Received 3,328 Upvotes on 2,987 Posts
I didn't bring that up since I'm not sure if both three way switches need a neutral. I'm not wiring them that way.

Four wire could be used from the last light to the switch and the neutral would be carried thru.
 
  #6  
Old 09-14-14, 07:56 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,413
Received 161 Upvotes on 141 Posts
Wiring the recessed that way also fills up the small wiring compartments and may be over the allowed fill for the boxes.
 
 