need to replace baseboard heater???
I need to replace a baseboard electric heater in bath, the circuit for this is a double 20 amp, there are no label on old heater and not sure what to go with , a 500 watt 240 volt 30 inch or a 350 watt 240/208 volt baseboard, would one of these work for me? also would a 22 amp 120/240 volt thermostate work with these , any help on this would be great thanks.:
#2
Welcome to the forums.
I would stay with the 500 watt heater. It will heat faster than the smaller unit.
500 watts at 240v is only a little over 2 amps so a 22 amp thermostat would work fine.
I would stay with the 500 watt heater. It will heat faster than the smaller unit.
500 watts at 240v is only a little over 2 amps so a 22 amp thermostat would work fine.
#3
circuit for this is a double 20 amp, there are no label on old heater and not sure what to go with , a 500 watt 240 volt 30 inch or a 350 watt 240/208 volt baseboard, would one of these work for me?
also would a 22 amp 120/240 volt thermostate work with these , any help on this would be great thanks.:
#4
How much heat is there now? It was probably sized for the heat loss for that room. Install one too small and it may not keep up.
#9
I have closed the other thread you started. What exactly confuses you about 208/240. That is simply the voltage range the heater will operate on. Any heater rated for 208 volts or 240 volts or both will work for you.
#10
looking at u unit that is 240/208 v , would this and the 22amp 120/240v themostat work for me you think?
Your 22A 120/240V thermostat will work on any 120V or 240V heater that uses less than 22A at 120 or 240V.
To calculate your amperage take your rated watts and divide by the rated voltage.*