multiwire circuit square D?


  #1  
Old 09-15-14, 06:09 PM
Q
Member
Thread Starter
Join Date: Jun 2014
Location: Canada
Posts: 1,660
Received 1 Upvote on 1 Post
multiwire circuit square D?

I have a Square D panel operating as a junction point (I think it was installed before the main panel).
This Square D is connected to a 50A 2 pole on the main panel.

It has a 2 pole breaker on it that I know is connected to the receptacle that the fridge is plugged into.
I recently changed changed the receptacle by the fridge but as the breaker is 2 pole it got me thinking:
- isn't it running 240v, 120 for each hot wire?
- if I connected both and forgot to remove the hot tab, would it trip?
- this could also be a multi wire circuit powering another circuit but the breaker panel is badly labelled and I haven't yet found another receptacle.
 
  #2  
Old 09-15-14, 06:12 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,941
Received 4,144 Upvotes on 3,722 Posts
Was the tab broken off of the old receptacle ?

If it was..... and you replaced it without breaking the tab off.... you'd have breakers tripping.
 
  #3  
Old 09-15-14, 06:31 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,481
Received 913 Upvotes on 771 Posts
- isn't it running 240v, 120 for each hot wire?
Yes, but you are forgetting it is sharing the neutral.

if I connected both and forgot to remove the hot tab, would it trip
Yes, and make quite a bang at the same time!
this could also be a multi wire circuit powering another circuit but the breaker panel is badly labelled and I haven't yet found another receptacle
That would be my guess.
 
 