Sub Panel

I am considering installing a Sub Panel in my garage and I have a few questions. I would like to run the wire myself and have an electrician hook it up at both ends to save some money.

I have 200 A service, but mostly gas appliances. The only major electrical appliance is a double 15 AC unit and a 30 A dryer.

In the garage I may want to eventually get an electric car years down the road which is 30A, I am thinking of buying a popup camper which needs up to 30A, I will have tools in there, plus I may add a small heat pump to the garage at some point in the future.

I was thinking 100A subpanel, but is that too big?
 
  #2  
Old 09-16-14, 06:16 AM
S
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 18,867
Received 1,186 Upvotes on 1,144 Posts
Welcome to the forums.

Nope, 100 amps does not sound too big but hang tight and the pros will chime in as well.
 
  #3  
Old 09-16-14, 07:09 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
I would like to run the wire myself and have an electrician hook it up
You may have a hard time finding an electrician to do that because of permits. He can't work on your homeowners permit and he wouldn't want to have you work on his permit because he would be liable for your mistakes. However connections aren't that difficult to learn.
 
  #4  
Old 09-16-14, 05:51 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,752
Received 672 Upvotes on 570 Posts
I agree with Mitch, 100 amp sounds just fine. Pick up a value pack 100 panel with a main breaker and you will get some breakers included for around $55 at big orange.

As for the hook ups, this is a DIY site you know. We can lead you on the proper path to DIY the task. Just ask.
 
  #5  
Old 09-19-14, 04:06 AM
M
Member
Thread Starter
Join Date: Sep 2014
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
So if I did this myself I have some questions. I have done wireing before and I have added breakers to a panel but nothing beyond 110.

1. It will likly be a 60 - 80 ft run, lets say 100 ft to be safe. What gauge wire do I need.
2. When hooking up the panel is it as simply as getting a double 100 A breaker to place in my original panel and hooking up one hot to each of the double breakers?
3. With that high of a current are their codes about how I should run the wire in my house?
 
  #6  
Old 09-19-14, 04:16 AM
M
Member
Thread Starter
Join Date: Sep 2014
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
I have one other question as well. I found that I would need 2 gauge wire for the temp and curent load I am looking for, but its strainded wire. I had always thought you used solid core wire because it has better electical resistance properties.
 
  #7  
Old 09-19-14, 05:07 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Stranded or solid have the same proprieties but #2 solid would be a real beatch to work with.
 

Last edited by ray2047; 09-19-14 at 07:06 AM.
  #8  
Old 09-19-14, 06:15 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,893
Received 163 Upvotes on 142 Posts
Conductors #8 and larger will all be stranded.
 
  #9  
Old 09-19-14, 07:08 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
It's been a long time, but I have seen solid #8 TW used a few times. Given the choice even back then, I don't know why anyone would have chosen solid over stranded unless maybe the job specs called for it.

I found that I would need 2 gauge wire for the temp and curent load I am looking for, but its strainded wire.
Given your application, I would use #3 THHN/THWN.
 
  #10  
Old 09-19-14, 07:36 AM
M
Member
Thread Starter
Join Date: Sep 2014
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
I chose #2 since it did 95 amps at 60C figured it was better to be safe on the temps. I will likly still go with it unless there is some reason not to have too large of a wire. I perfer to over engineer my projects.
 
  #11  
Old 09-19-14, 07:43 AM
M
Member
Thread Starter
Join Date: Sep 2014
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
So here would be my setup
100 amp breaker in main box
#2 wire about 60 ft to garage. Part will go in an unheated crawl space will that be an issue?
100 amp sub panel in garage with a secondary main breaker (only because the box comes with one)

Anything special I need to know about wireing it through my basement? Its finished but I have no issues removing drywal.
 
  #12  
Old 09-19-14, 08:05 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
The EGC (ground to sub) wire can be #8.
how I should run the wire in my house
In conduit or use cable through the walls.

Just to verify you bought and added a ground bar to the subpanel, unbounded the neutral bar, and have the #6 wire to your ground rod at the subpanel?
 
  #13  
Old 09-19-14, 08:20 AM
M
Member
Thread Starter
Join Date: Sep 2014
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
"Just to verify you bought and added a ground bar to the subpanel, unbounded the neutral bar, and have the #6 wire to your ground rod at the subpanel?"

I am still in the planning phase but yeah I have not done any of that.

The more I think about this the more I am just going to pay someone to run the sub panel to the garage becasue there is just too much I do not know, plus my main panel is new and I do not want to void anything.
Then I will wire the garage up myself becasue that I know how to do.
 
 