30 amp 240v circuit with 120v outlet.

Reply

  #1  
Old 09-20-14, 07:11 PM
Member
Thread Starter
Join Date: Aug 2009
Location: USA
Posts: 4,941
30 amp 240v circuit with 120v outlet.

Let's say I need a 240v circuit. I run 10-3 to my 240v receptacle. Can I then install a 120v receptacle using the neutral wire one one of the hots from the 10-3?
 
Sponsored Links
  #2  
Old 09-20-14, 07:15 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,968
In theory, yes. In practicality, no. You have 30 amp OCP, which will be too much for the 120 volt receptacle, and it would be a bear bending 10 gauge wire inside a box and connect it to the receptacle.
 
  #3  
Old 09-20-14, 07:55 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,050
Though not recommending it you could use a fused receptacle with a 15 amp fuse and probably meet code.

Name:  z9DjG73LJpu0X0YVQloBoQ_m.jpg
Views: 419
Size:  16.0 KB
Image source: quizlet.com
 
  #4  
Old 09-20-14, 10:24 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,546
In theory, yes. In practicality, no. You have 30 amp OCP, which will be too much for the 120 volt receptacle, and it would be a bear bending 10 gauge wire inside a box and connect it to the receptacle.

Who said he's not using a 30A 120V receptacle?

Assuming you use a 30A receptacle, you can do that no problem.
 
  #5  
Old 09-21-14, 04:37 AM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,968
True, but walk around your house and write down the number of 30 amp 120 volt receptacles you have. Or the practical applications.
 