Running wires across RAFTERS?

Is it ok to run all of my electrical wires across attic rafters. I am asking this because I think it would be easier on me when re-wiring my house. We currently have the old 2 wire/no ground and a 100 AMP breaker box with some seriously lethal wiring work that I need to get rid of asap.
I am planning on home runs for each room. So, it would make it easier on me to not lift up all the insulation that has rat poop and lay new wires, I just want to run the new ones across the rafters and to their respective locations.

So there is no confusion, I exactly mean running lines across the rafters (Not through) and securing them as per the code.

Of course the path would be all the way from the receptacle, up the inside of the wall, to the attic, and across the rafters and then back down through the wall to the circuit breaker box.

I appreciate all input on this. The code, the opinions, and the experience. First please answer the code though. Is this legal.
 
Attached Images  
  #2  
Old 09-21-14, 06:44 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,759
Received 676 Upvotes on 573 Posts
Yes, that is fine. NEC wise it would also be OK to drill the rafters and run the cable through them. As long as they are at least a 1 1/4" away from the nailing face of the rafter. I would keep them greater than that though.
 
  #3  
Old 09-21-14, 06:49 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
“Is this attic accsessable?320.23 In Accessible Attics. Type AC cables in accessible attics or roof spaces shall be installed as specified in 320.23(A) and (B).
(A) Cables Run Across the Top of Floor Joists. Where run across the top of floor joists, or within 2.1 m (7 ft) of the floor or floor joists across the face of rafters or studding, the cable shall be protected by guard strips that are at least as high as the cable. Where this space is not accessible by permanent stairs or ladders, protection shall only be required within 1.8 m (6 ft) of the nearest edge of the scuttle hole or attic entrance”

Excerpt From: National Fire Protection Association (NFPA). “NFPA 70®, National Electrical Code® (NEC®), 2014 Edition.” NFPA. iBooks.
This material may be protected by copyright.

Check out this book on the iBooks Store: https://itunes.apple.com/WebObjects/...k?id=712925892
 
  #4  
Old 09-21-14, 11:01 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,895
Received 163 Upvotes on 142 Posts
Just to clarify, rafters can be drilled, trusses cannot be drilled.
 
  #5  
Old 09-22-14, 02:45 AM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,608
Upvotes: 0
Received 9 Upvotes on 8 Posts
I would build a raceway of three 2x4's running atop the joists. Lay in all your cables and exit the bottom of the raceway as needed to the application. It will provide the needed protection and will keep all the cabling together in a neat way.
 
 