I have a 60 amp subpanel about 2 foot from the main box and have it connected by 6ga wire. My question is, if I replace the 60 amp with a 125 amp rated but only install a 100 amp breaker what size wire would I need. Also the sub box has only 1 ground bar and needs second one; is it connected directly to box or is it separated from the box using rubber or plastic standoffs like it's original one, thanks.
 
  #2  
Old 09-26-14, 09:11 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
#3 copper for 100 amps, four wires.
Also the sub box has only 1 ground bar and needs second one; is it connected directly to box or is it separated from the box using rubber or plastic standoffs like it's original one,
The original one on insulators is not a ground bar. It is a neutral bar. What you install will be a ground bar and be bonded to the subpanel case by directly mounting metal to metal. The neutral bar in the subpanel is isolated. If it has a bonding screw or strap that is removed.
 
 