2 breakers in same box or split outlet?
I'm installing a new washer and dryer and I'd like dedicated circuits for each. If I'm using a tie down bar, can I put outlets from two different breakers in the same box?
One more. Same as above, and can I put them on a split receptacle (lower powered by one circuit, upper by another)?
Thanks
One more. Same as above, and can I put them on a split receptacle (lower powered by one circuit, upper by another)?
Thanks
#4
But why
#6
If you are using a multi-wire branch circuit the handles need to be tied or a two pole breaker used.
#7
can I put them on a split receptacle (lower powered by one circuit, upper by another)?
#8
Member
Thread Starter
Join Date: Jan 2012
Location: United States
Posts: 84
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Handyone
But why
But why
Quote from Ray above. Why? It's good you're tying breakers. But as a courtesy/warning to others, I would still take a permanent marker and mark backside of face plate "warning, this box contains two circuits".
Which begs the question, is it okay to have them on the same 120amp breaker even though the manufacturer reccos separate (dryer IS gas).
If you have two circuits on the same yoke the breaker handles must be tied (or use 2 pole breaker) regardless of whether it is a multiwire branch circuit or not.
Thanks all for the help.
#9
Normally only one (duplex) receptacle on one breaker is used for the dryer and washer. Just run a 20 amp circuit. It should be fine. Just as long as the amps of the dryer and washer added together is 16 amps or less you should be fine. Or is this a dryer with special features like steam.
Or as others suggested just run a multiwire circuit.
Pros, if he runs a 20 amp multi wire circuit will the one receptacle rule apply requiring a NEMA 5-20R?
Or as others suggested just run a multiwire circuit.
Pros, if he runs a 20 amp multi wire circuit will the one receptacle rule apply requiring a NEMA 5-20R?
Last edited by ray2047; 09-28-14 at 11:12 PM.