I'm installing a new washer and dryer and I'd like dedicated circuits for each. If I'm using a tie down bar, can I put outlets from two different breakers in the same box?

One more. Same as above, and can I put them on a split receptacle (lower powered by one circuit, upper by another)?

Thanks
 
  #2  
Old 09-28-14, 03:24 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Either way will be okay but why? Usually they can both be on the same breaker.
 

Last edited by ray2047; 09-28-14 at 09:32 PM. Reason: Remove wrong information.
  #3  
Old 09-28-14, 03:31 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,607
Upvotes: 0
Received 9 Upvotes on 8 Posts
Assuming it is a gas dryer.
 
  #4  
Old 09-28-14, 06:04 PM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
But why
Quote from Ray above. Why? It's good you're tying breakers. But as a courtesy/warning to others, I would still take a permanent marker and mark backside of face plate "warning, this box contains two circuits".
 
  #5  
Old 09-28-14, 07:41 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,272
Upvotes: 0
Received 1 Upvote on 1 Post
I would also use 12-3 to make it easier to identify.
 
  #6  
Old 09-28-14, 07:43 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,933
Received 180 Upvotes on 158 Posts
If you are using a multi-wire branch circuit the handles need to be tied or a two pole breaker used.
 
  #7  
Old 09-28-14, 09:01 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,839
Received 178 Upvotes on 161 Posts
can I put them on a split receptacle (lower powered by one circuit, upper by another)?
If you have two circuits on the same yoke the breaker handles must be tied (or use 2 pole breaker) regardless of whether it is a multiwire branch circuit or not.
 
  #8  
Old 09-28-14, 10:15 PM
S
Member
Thread Starter
Join Date: Jan 2012
Location: United States
Posts: 84
Upvotes: 0
Received 0 Upvotes on 0 Posts
Handyone
But why
Quote from Ray above. Why? It's good you're tying breakers. But as a courtesy/warning to others, I would still take a permanent marker and mark backside of face plate "warning, this box contains two circuits".
I think Ray may have been asking why two breakers, not why would I tie them.

Which begs the question, is it okay to have them on the same 120amp breaker even though the manufacturer reccos separate (dryer IS gas).

If you have two circuits on the same yoke the breaker handles must be tied (or use 2 pole breaker) regardless of whether it is a multiwire branch circuit or not.
Would you suggest using a shared neutral with 12/3? Or if I went this route, so I just use 12/2 for both and treat them as if they are on different receptacles?

Thanks all for the help.
 
  #9  
Old 09-28-14, 10:47 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Normally only one (duplex) receptacle on one breaker is used for the dryer and washer. Just run a 20 amp circuit. It should be fine. Just as long as the amps of the dryer and washer added together is 16 amps or less you should be fine. Or is this a dryer with special features like steam.

Or as others suggested just run a multiwire circuit.

Pros, if he runs a 20 amp multi wire circuit will the one receptacle rule apply requiring a NEMA 5-20R?
 

Last edited by ray2047; 09-28-14 at 11:12 PM.
  #10  
Old 09-29-14, 09:06 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,839
Received 178 Upvotes on 161 Posts
if he runs a 20 amp multi wire circuit will the one receptacle rule apply requiring a NEMA 5-20R?
My opinion is yes, the split wired duplex receptacle will have to be rated at 20 amps.
 
  #11  
Old 09-29-14, 07:26 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,272
Upvotes: 0
Received 1 Upvote on 1 Post
Now that I'm thinking about this, you may want to use 2 20A single receptacles as some washers and dryers have angled plugs. What I would personally do is run 12/3 on a 2 pole 20a breaker, into a 2 gang box feeding 2 single receptacles. Use a gfci breaker if gfci protection is required.
 
 