Another garage sub panel question

I have read many of the posts here, just wanted a bit more advice. I need to run 165 ft from my main panel to my RV garage. Its mainly for keeping the battery charged in the RV, a few lights and a few plugs. No plan to run the ac units on the RV, so I figured 50 amps would suffice. I have conduit already run under the driveway.

Would this wire suffice: 6/3 W/ GROUND ROMEX SIMPULL WIRE. THIS WIRE HAS 3 INSULATED CONDUCTORS AND 1 BARE GROUND CONDUCTOR AND IS RATED FOR 60 AMPS.

BTW, I am located in TX, in an area with no inspections. I will do this myself, Just want to be safe and get others opinions....
 
  #2  
Old 09-30-14, 12:22 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,980
Received 196 Upvotes on 172 Posts
Type NM cable cannot be used outdoors, even if in conduit.
 
  #3  
Old 09-30-14, 12:39 PM
G
Member
Thread Starter
Join Date: Sep 2014
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
okay, got it...no NM..this appears to be suitable: 2-2-2-4 Aluminum SER Wire..?
 
  #4  
Old 09-30-14, 12:43 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
It is best practice to use individual conductors such as THWN not cable. (Cable, especially that large, can be hard to pull.) You would need one #6 white, two #6 black*, and one #10 green. Conduit must be buried 18" minimum.

*You can use one black, one red instead of two black but color doesn't really matter as long as it isn't white gray or green.)

Are you planning to use a 100 amp Main Breaker panel for the subpanel?
 
  #5  
Old 09-30-14, 01:04 PM
G
Member
Thread Starter
Join Date: Sep 2014
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
OK....THWN it is, the same thing I used years ago when I ran a panel for my hot tub. I used all black then as that was all Home depot had.....same thing now, all they show online per foot is black, the #10 is available in green....

I planned on using a 50 amp breaker sub panel.

I used white tape to mark the ends....do you see any issue with that?
 
  #6  
Old 09-30-14, 02:57 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,980
Received 196 Upvotes on 172 Posts
Conductors smaller than #4 are supposed to have the correct color insulation. Re-identification is allowed on larger conductors with tape or paint.

Given the loads you listed a panel with a 20 or 30 amp feed would suit your needs.
 
  #7  
Old 10-01-14, 07:15 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,874
Received 185 Upvotes on 166 Posts
OK....THWN it is, the same thing I used years ago when I ran a panel for my hot tub. I used all black then as that was all Home depot had.....same thing now, all they show online per foot is black, the #10 is available in green....
I'd be willing to bet that the store actually stocks colors in the #6 THHN/THWN wire even though they may only show black on their website. Why not call them and ask?
 
 