Please settle a bet I have with my brother in law.
We have 100A. Use #3CU I believe. Can the neutral service wire be sized smaller?
We have 100A. Use #3CU I believe. Can the neutral service wire be sized smaller?
#3
The neutral must be sized to handle any unbalanced load.
#4
We have 100A. Use #3CU I believe. Can the neutral service wire be sized smaller?
#5
Member
hmmm; 220.61 provides for reduced neutral size, but ONLY IF you can prove the maximum possible unbalanced load is accommodated by the ampacity of the so-called neutral conductor. For instance, if you have several 240V and 120V loads, you may calculate the worst case load on one side of the service using only the 120V loads. So, I take this to mean that if you have 5, 20 AMP 120V branch breakers on one side of your panel you MAY NOT reduce the neutral size on a 100A service. If you have 2 x 15A and 2 x 20A breakers on the worst case side then you may size for 70 AMP, since that would be your worse case unbalanced load.
However, Table 310.15 B 6 starts service ampacity at 100Amps and #4 copper; calling for a #6 neutral may raise questions from the inspector to prove this case, and I would not find this risk acceptable given the $ savings. Larger services have more value in doing the neutral reduction.
The OP needs to know the insulation of the #3, in any case. I've seen in the field a #4 Cu TW feeding a 100A breaker, which is not correct with a non-motor load.
However, Table 310.15 B 6 starts service ampacity at 100Amps and #4 copper; calling for a #6 neutral may raise questions from the inspector to prove this case, and I would not find this risk acceptable given the $ savings. Larger services have more value in doing the neutral reduction.
The OP needs to know the insulation of the #3, in any case. I've seen in the field a #4 Cu TW feeding a 100A breaker, which is not correct with a non-motor load.