Neutral size?


  #1  
Old 10-03-14, 05:26 PM
Z
Member
Thread Starter
Join Date: Oct 2013
Posts: 487
Upvotes: 0
Received 0 Upvotes on 0 Posts
Neutral size?

Please settle a bet I have with my brother in law.

We have 100A. Use #3CU I believe. Can the neutral service wire be sized smaller?
 
  #2  
Old 10-03-14, 05:43 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,608
Upvotes: 0
Received 9 Upvotes on 8 Posts
Neutral is same size. Grounding conductor can be one size smaller in certain instances. The neutral must be sized to handle any unbalanced load.
 
  #3  
Old 10-03-14, 06:22 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,098
Received 3,609 Upvotes on 3,235 Posts
The neutral must be sized to handle any unbalanced load.
Just to add to that..... any unbalanced load and right up to 100A.
 
  #4  
Old 10-03-14, 07:11 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,827
Received 178 Upvotes on 161 Posts
We have 100A. Use #3CU I believe. Can the neutral service wire be sized smaller?
The answer is YES! You may have #3 copper conductors in your 100 amp residential service, but #4 copper is all that is required by the NEC. The neutral conductor could be a #4 and it would be smaller and still be legal. That being said, I am not a fan of reducing neutrals and wouldn't do it even on a 200 amp service.
 
  #5  
Old 10-04-14, 07:09 AM
T
Member
Join Date: Oct 2005
Location: USA
Posts: 1,561
Received 74 Upvotes on 69 Posts
hmmm; 220.61 provides for reduced neutral size, but ONLY IF you can prove the maximum possible unbalanced load is accommodated by the ampacity of the so-called neutral conductor. For instance, if you have several 240V and 120V loads, you may calculate the worst case load on one side of the service using only the 120V loads. So, I take this to mean that if you have 5, 20 AMP 120V branch breakers on one side of your panel you MAY NOT reduce the neutral size on a 100A service. If you have 2 x 15A and 2 x 20A breakers on the worst case side then you may size for 70 AMP, since that would be your worse case unbalanced load.
However, Table 310.15 B 6 starts service ampacity at 100Amps and #4 copper; calling for a #6 neutral may raise questions from the inspector to prove this case, and I would not find this risk acceptable given the $ savings. Larger services have more value in doing the neutral reduction.

The OP needs to know the insulation of the #3, in any case. I've seen in the field a #4 Cu TW feeding a 100A breaker, which is not correct with a non-motor load.
 
 