Breaker off...still have 10V at switch?


  #1  
Old 10-06-14, 09:19 AM
R
Member
Thread Starter
Join Date: Oct 2014
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
Breaker off...still have 10V at switch?

Any idea why I would still have 10V AC at a wall switch, from Hot to GND, even with breaker turned off?
 
  #2  
Old 10-06-14, 09:24 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Classic symptom of using a digital multimeter instead of an analog multimeter. If you are using a digital it isn't real. Just a induced or capacitive voltage the digital's impedance is to high to bleed off.
 
  #3  
Old 10-06-14, 09:30 AM
R
Member
Thread Starter
Join Date: Oct 2014
Posts: 9
Upvotes: 0
Received 0 Upvotes on 0 Posts
OK, thanks Ray! Since the circuits are working properly with the breaker on, this eases my mind.
 
 