Will I be able to run this welder? 20 amp in a 15 amp breaker

Will I be able to run this welder? 20 amp in a 15 amp breaker


  #1  
Old 10-10-14, 03:57 PM
M
Member
Thread Starter
Join Date: Oct 2014
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Will I be able to run this welder? 20 amp in a 15 amp breaker

I would like to buy a 120V welder, 60 Hz, 20 amps, single phase input.

My garage (where it will be used) has a 15 amp breaker. It also runs the lights in the garage and the lights in the kitchen. Even with all the lights turned off, will I be able to use this welder without tripping the breaker? I'm not sure if the 20 amps is the max it will use and the average amps used is under that, or if it needs a constant 20 amps.

Any input?

Thanks
 
  #2  
Old 10-10-14, 04:10 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Give us the make and model number of the welder.
 
  #3  
Old 10-10-14, 04:11 PM
Mr.Awesome's Avatar
Member
Join Date: Oct 2013
Location: Canada
Posts: 511
Received 0 Upvotes on 0 Posts
Thats a big negative. I'm sure it might run for you if you tried it, but your breaker, wire, and receptacle are not rated for what you would be using it for. Time to plan out how you're going to install a dedicated 20A receptacle in the garage.
 
  #4  
Old 10-10-14, 04:43 PM
M
Member
Thread Starter
Join Date: Oct 2014
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
  #5  
Old 10-10-14, 06:16 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
Is your garage attached to your house or detached?
 
  #6  
Old 10-10-14, 09:41 PM
M
Member
Thread Starter
Join Date: Oct 2014
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
The garage is attached.

Just curious now, but why a 30 amp? If it's for a 20amp, why wouldn't a 20 amp work? Because of the extra amps the lights that the breaker is wired too also?

Thanks!!
 
  #7  
Old 10-10-14, 10:22 PM
Justin Smith's Avatar
Member
Join Date: Dec 2010
Location: Cressona, Pa, USA
Posts: 2,272
Upvotes: 0
Received 1 Upvote on 1 Post
Based on the 20% duty cycle, a 20A 120V circuit with a 20A single receptacle on a 20A gfci breaker should be fine.
 
  #8  
Old 10-10-14, 11:15 PM
M
Member
Thread Starter
Join Date: Oct 2014
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
I have a 15 amp breaker though. With the 20% duty cycle, will I be alright?
 
  #9  
Old 10-11-14, 06:11 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
My garage (where it will be used) has a 15 amp breaker. It also runs the lights in the garage and the lights in the kitchen. Even with all the lights turned off, will I be able to use this welder without tripping the breaker? I'm not sure if the 20 amps is the max it will use and the average amps used is under that, or if it needs a constant 20 amps.
You might be able to do very light welding without tripping the 15 amp breaker, but why risk it? It cannot be that hard to install a 20 amp circuit to an attached garage.
 
  #10  
Old 10-11-14, 06:38 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,756
Received 675 Upvotes on 573 Posts
I have a Clark 120 volt MIG which will run on a 15 amp circuit for a little while. It will trip the circuit if I push it too long. It has not problems on a 20 amp circuit.

The plug on the unit you linked to has a 15 amp cord so I suspect it will run about the same as mine.

From your manual:

Flip the Power Switch to the OFF position, then plug
the Welder into a dedicated, 120 V~, 20 A circuit
with delayed action type circuit breaker or fuses.
 
  #11  
Old 10-16-14, 02:09 PM
E
Member
Join Date: Oct 2014
Location: USA
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Chances are that this is a no go. The next questions is, what gauge wire was used? Depending on the length of the total run and the gauge of wire used, you may just be able to upgrade the breakers and the outlet.
 
 