Garage Door Openers Trip GFI Outlet...High Amp options?

I have a rental home that the tenants complain that they frequently need to reset the GFI outlet. Is there a higher-amp GFI outlet available? I could replace the GFI with a normal outlet, but that might be a code violation.
 
  #2  
Old 10-13-14, 02:02 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
GFCI s do not trip because of over amperage. Try replacing the GFCI receptacle. If the GDO continues to trip it is either the wiring or the GDO that is bad. Is the GDO plugged directly in to the receptacle that trips or is an extension cord used?
 
  #3  
Old 10-14-14, 05:15 AM
B
Member
Thread Starter
Join Date: Aug 2002
Location: US
Posts: 45
Upvotes: 0
Received 0 Upvotes on 0 Posts
I'll try replacing it. It would be a low cost attempt to fix the problem.
 
  #4  
Old 10-14-14, 08:26 AM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,607
Upvotes: 0
Received 9 Upvotes on 8 Posts
As long as it is a ceiling mounted receptacle, would it even need GFCI protection?
 
  #5  
Old 10-14-14, 09:14 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
... ceiling mounted receptacle, would it even need GFCI protection?
Under most recent code, yes, but the actual GFCI protection would have to be in easy reach so the actual receptacle for the GDO non GFCI supplied by a GFCI breaker or receptacle or blank GFCI.
 
  #6  
Old 10-14-14, 05:37 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
I believe it was the 2008 NEC that required all garage receptacles, including on the ceiling for GDO, to be GFCI protected.
 
  #7  
Old 10-14-14, 05:53 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
The one caveat is that the gfi must be readily accessible. It cannot be ceiling mounted.
 
 