Main breaker panel breakers movement when pressed.
#1
Member
Thread Starter
Join Date: Dec 2008
Location: USA
Posts: 112
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Main breaker panel breakers movement when pressed.
How snug should breakers be?
I was surprised when I pressed on the outside edge of a breaker that it moved a little.
I thought maybe it's not inserted all the way. Took the cover off and checked that it is fully slid into the tab on the outer edge and that when pressing it towards the inside that it is in all the way.
It looked just as all the breakers do. So I pressed on all the breakers and they wiggle just about as much as the first one.
I've never messed with my box before so I found this surprising.
Is this normal?
These are this type of breaker:
Siemens Recalls Circuit Breakers Due to Fire Hazard | CPSC.gov
Of which I had found a recall for Siemens breakers. I'll have them checked out to be sure they aren't of the batch of bad ones.
Good thing I looked this stuff over. Just moved here recently and I'm really ticked that the home inspector missed a few things.
I noticed that there are 2 20 amp breakers that are on 15 amp circuits. Wow. I think if there's one thing he should have checked, was that. Waste of money.
Thanks in advance for any reply.
I was surprised when I pressed on the outside edge of a breaker that it moved a little.
I thought maybe it's not inserted all the way. Took the cover off and checked that it is fully slid into the tab on the outer edge and that when pressing it towards the inside that it is in all the way.
It looked just as all the breakers do. So I pressed on all the breakers and they wiggle just about as much as the first one.
I've never messed with my box before so I found this surprising.
Is this normal?
These are this type of breaker:
Siemens Recalls Circuit Breakers Due to Fire Hazard | CPSC.gov
Of which I had found a recall for Siemens breakers. I'll have them checked out to be sure they aren't of the batch of bad ones.
Good thing I looked this stuff over. Just moved here recently and I'm really ticked that the home inspector missed a few things.
I noticed that there are 2 20 amp breakers that are on 15 amp circuits. Wow. I think if there's one thing he should have checked, was that. Waste of money.
Thanks in advance for any reply.
#3
It's normal for the breakers to fit loosely in the panel. Most covers are cut out to tightly fit around the circumference of all the breakers and hold them in place.
#5
Member
Thread Starter
Join Date: Dec 2008
Location: USA
Posts: 112
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I checked the gauge of the wire into it and it's a #12.
My 20amp breaker has a #10 in it, as I checked it also.
The breaker in question(20amp w/#12 wire) has a microwave oven on it and a dishwasher on it. Plus two 20-amp GFCI twin outlets above the kitchen counter top ends. There is a coffee pot and a toaster that are plugged into those 20 amp outlets.
Thanks for the feedback.
My 20amp breaker has a #10 in it, as I checked it also.
The breaker in question(20amp w/#12 wire) has a microwave oven on it and a dishwasher on it. Plus two 20-amp GFCI twin outlets above the kitchen counter top ends. There is a coffee pot and a toaster that are plugged into those 20 amp outlets.
Thanks for the feedback.

#6
The countertop receptacle circuits should not feed the dishwasher. If the MW is over the range it should be on a dedicated circuit.
#7
You can get blanks if there are missing breaker knockouts in your panel cover. These blanks take the place and are the same size as a breaker. They also keep fingers out.
#8
Member
Thread Starter
Join Date: Dec 2008
Location: USA
Posts: 112
Upvotes: 0
Received 0 Upvotes
on
0 Posts
The countertop receptacle circuits should not feed the dishwasher. If the MW is over the range it should be on a dedicated circuit.
Read more: http://www.doityourself.com/forum/el...#ixzz3GVqfrx3c
Read more: http://www.doityourself.com/forum/el...#ixzz3GVqfrx3c
My biggest concern is that #12 wire supporting 20 amps.
#9
Member
Thread Starter
Join Date: Dec 2008
Location: USA
Posts: 112
Upvotes: 0
Received 0 Upvotes
on
0 Posts
You can get blanks if there are missing breaker knockouts in your panel cover. These blanks take the place and are the same size as a breaker. They also keep fingers out.