Need help with diagnosis
#1
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 31
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Need help with diagnosis
Yesterday my master bedroom circuit got finicky. Turned on the vacuum cleaner, everything died. The breaker did not switch to off, but I switched it off and then on, and things worked again. The problem continued, with smaller and smaller voltages blowing the breaker. Once, the power even tried to flicker back on a few times on its own. Then today, absolutely nothing working on that circuit. Turned everything off, and flipped the breaker. Even LEDs on the switches didn't light. Volt meter shows same voltage to that breaker as all of the others. Replaced the breaker, anyway. No difference. Volt probe shows that (some) current is getting to all switches and outlets. Receptacle tester doesn't light at all.
I would be very grateful for any advice.
Thanks!
I would be very grateful for any advice.
Thanks!
#2
Welcome to the forums! I know you have a plug in detector, and possibly a proximity tester. Both are limited in their accuracy to do good testing. Is your volt meter digital or analog? Analog is better and is not susceptible to phantom voltages.
A likely scenario is your receptacles have stab back connections which are suspect at best. If you can determine the first receptacle in line from your panel, remove the power from the circuit, and pull the receptacle from the box, you may find one or more of the stab back wires have become loose. Let us know what you find there.
A likely scenario is your receptacles have stab back connections which are suspect at best. If you can determine the first receptacle in line from your panel, remove the power from the circuit, and pull the receptacle from the box, you may find one or more of the stab back wires have become loose. Let us know what you find there.
#3
I just to get come terminology straight so we all know what you are referring to:
Voltage does not trip a breaker, amps (or current) does.
A voltage probe only shows you have voltage, it does not tell you anything about current. For that you need a clamp on meter.
When a circuit breaker trips, it will not trip to off, it trips to the middle position. You then have to turn it to off, then back to on.
Follow Chandlers direction and post back and we can help you further.
Voltage does not trip a breaker, amps (or current) does.
A voltage probe only shows you have voltage, it does not tell you anything about current. For that you need a clamp on meter.
When a circuit breaker trips, it will not trip to off, it trips to the middle position. You then have to turn it to off, then back to on.
Follow Chandlers direction and post back and we can help you further.

#4
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 31
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks guys. More to think about.
The breaker didn't even trip to the middle position. I don't know if that matters.
The circuit is comprised of two different constructions. Original in 1957. Last year we had some built in closets added, and code required outlets on those outer walls. The 1957 outlets weren't three-prong, of course. And I'm ass-u-ming that the new ones are (true) three prong. Does that give us (you - really) any idea which is the first outlet? I'm guessing that the first outlet would be the (only remaining) original, which has a rat's nest of charger wires on it. I'm also guessing that the electrician pulled from those wires for the new outlets and lights. But if the originals didn't have the third prong, how did they get that extra ground?
I'll be attacking this again in the morning!
Thanks, again!
The breaker didn't even trip to the middle position. I don't know if that matters.
The circuit is comprised of two different constructions. Original in 1957. Last year we had some built in closets added, and code required outlets on those outer walls. The 1957 outlets weren't three-prong, of course. And I'm ass-u-ming that the new ones are (true) three prong. Does that give us (you - really) any idea which is the first outlet? I'm guessing that the first outlet would be the (only remaining) original, which has a rat's nest of charger wires on it. I'm also guessing that the electrician pulled from those wires for the new outlets and lights. But if the originals didn't have the third prong, how did they get that extra ground?
I'll be attacking this again in the morning!
Thanks, again!
#5
Turn off the circuit and see what receptacles turn off with your tester. Turn the circuit back on and recheck. The live one that is closest to the dead ones is the first one to check. The 2nd would be the first dead one. After that is might be a bit of an Easter egg hunt.
#6
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 31
Upvotes: 0
Received 0 Upvotes
on
0 Posts
If I had done this while things were working even a little, that would have helped. Now everything on that circuit is completely dead. I think it's easter egg hunt time. Unfortunately the likely culprit (the old one) requires moving the most furniture!
Thanks for the assist!
Thanks for the assist!
#7
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 31
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Well, I replaced the first outlet, and no joy. Still no more than trace voltage in that one, as well as all of the others. Tomorrow - the ceiling light. After that the hall ceiling fan. Fingers crossed!
#12
Temporarily Suspended
Join Date: Jul 2008
Location: NY
Posts: 10,265
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I would look in the attic first. Sometimes, BX was used when the house was built & Romex was used for additions. That's one way to differentiate between the two.
#16
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 31
Upvotes: 0
Received 0 Upvotes
on
0 Posts
New Question
Okay, guys. New question. I pulled the staple, inspected the wires, no apparent breaks. Separated the wires and powered up. Everything works beautifully. I would really like not to have to splice and install a junction box in such a godawful spot. What are my other options? (As a homeowner - I know you have other requirements.)
Thanks for all of the help!
Maureen
Thanks for all of the help!
Maureen
#17
Sorry to inform you that the splice needs to be made in an accessible junction box with a cover.
#19
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 31
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Curiouser and curiouser
I hope you guys are still tuned in.
After pulling the staple and inspecting the wires, I just separated the wires, turned the breaker back on, and everything worked perfectly. Two days later, the whole thing started up again. Flip a light switch, quick flash, then everything on the circuit is dead. Nothing is on that circuit but a ceiling light, a ceiling fan and light, and some outlets that have clocks and cell phone chargers on them. Went to the ceiling fan, thinking maybe that was the problem, since it had been wobbling for a while since we just installed it with a light box, not a ceiling fan box. Removed the fan. Had 55 volts between the black wire and the box. 65 between the wire nut (two blacks and a white) and the box. Just now, after dark, have less than 20 volts between the dangling black and the box. Wire nut to box is still 65. Found resistance in one 3 way switch, so replaced them both. No change.
BTW - replaced the circuit breaker as my first guess before I posted the original posting.
After pulling the staple and inspecting the wires, I just separated the wires, turned the breaker back on, and everything worked perfectly. Two days later, the whole thing started up again. Flip a light switch, quick flash, then everything on the circuit is dead. Nothing is on that circuit but a ceiling light, a ceiling fan and light, and some outlets that have clocks and cell phone chargers on them. Went to the ceiling fan, thinking maybe that was the problem, since it had been wobbling for a while since we just installed it with a light box, not a ceiling fan box. Removed the fan. Had 55 volts between the black wire and the box. 65 between the wire nut (two blacks and a white) and the box. Just now, after dark, have less than 20 volts between the dangling black and the box. Wire nut to box is still 65. Found resistance in one 3 way switch, so replaced them both. No change.
BTW - replaced the circuit breaker as my first guess before I posted the original posting.
#20
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 31
Upvotes: 0
Received 0 Upvotes
on
0 Posts
And another thing
Another weird thing was that the voltage probe lit up right away on all switches except one. One of the three way switches took several minutes to light up the probe.
#21
Another weird thing was that the voltage probe lit up right away on all switches except one.
Have you checked the repair splice you made?
#23
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 31
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I did not make a splice. The wires appeared to be in good condition, so I just separated them (since the sheathing was gone) to come back to at a later date. All was well for several days. Went back up to check them after the whole thing crashed again, and they were as I left them.
The 3 way with the high resistance appeared to be original. The 3 way that had minor resistance was replaced about 15 years ago. Replaced both. - Yes, marked the connections to ensure the right loops.
The 3 way with the high resistance appeared to be original. The 3 way that had minor resistance was replaced about 15 years ago. Replaced both. - Yes, marked the connections to ensure the right loops.
#24
You need to hire an electrician to do this properly. Whether the lights work or not... you have exposed wiring that need to be put into an accessible junction box. Your guesswork and finger crossing is not going to make this right.... time to open the phone book.
#26
Member
Join Date: Jan 2014
Location: USA
Posts: 630
Upvotes: 0
Received 0 Upvotes
on
0 Posts
A cousin of mine had squirrels get into his attic and eat the insulation on some of the Romex . They ate through a few of the copper sires , to . I had more than one extended phone call from him , untill he finally found the problems / bad spots . He lives about 6 hours away .
It can truly be an Easter Egg hunt . :-(
God bless
Wyr
It can truly be an Easter Egg hunt . :-(
God bless
Wyr
#28
DD, why are all your responses "hire an electrician"??? This does not require such services as it is totally DIY. We can help with the repairs, since this is obviously a DIY site and not a referral center. When the OP decides to fix it, we can help out.
#30
I did pull a squirrel out last winter.
#32
Member
Thread Starter
Join Date: Oct 2014
Location: USA
Posts: 31
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yeah, Joe. It was some pressure fit soffit vents that didn't pressure fit so well when the weather got cold and dry.
We've spent a fair amount of time in the attic inspecting wires, digging through insulation. The main reason for dealing with this ourselves right now is that I really can't see paying an electrician to do that kind of work. When things get technical, I'm very happy to back out and let a professional do the rest.
As we dig out and trace every damned wire, it would be great to have some way of protecting them for the future. Is there some kind of split conduit that I can cover the wires with as I go?
We've spent a fair amount of time in the attic inspecting wires, digging through insulation. The main reason for dealing with this ourselves right now is that I really can't see paying an electrician to do that kind of work. When things get technical, I'm very happy to back out and let a professional do the rest.
As we dig out and trace every damned wire, it would be great to have some way of protecting them for the future. Is there some kind of split conduit that I can cover the wires with as I go?
#33
As we dig out and trace every damned wire, it would be great to have some way of protecting them for the future. Is there some kind of split conduit that I can cover the wires with as I go?