Electric heater at new house - shock

At my recently purchase house there is electric heat in each room. The electric heater in the living room often shocks you if I touch the metal cover or screw. I even got shocked cleaning up dog pee from the floor next to the heater. I pulled the covers off of it and I don't see anything glaring that's wrong with it other then a spot shown in the 3rd photo that looks like it got hot there. I'll attach a few photos for you to see or if you know what's causing this please give me some insight. We have pets and a little boy so it's important to me. Thanks

Name:  image.jpg
Views: 323
Size:  35.5 KB

Name:  image.jpg
Views: 358
Size:  36.5 KB

Name:  image.jpg
Views: 327
Size:  34.4 KB
 
Sponsored Links
  #2  
Old 11-04-14, 05:12 PM
Mr.Awesome's Avatar
Member
Join Date: Oct 2013
Location: Canada
Posts: 592
Received 0 Votes on 0 Posts
Do you see any bare wires without casing on them where the wires enter?
It sounds like you're missing a bond and have a small nick in one of your hots somewhere.
 
  #3  
Old 11-04-14, 05:17 PM
Member
Thread Starter
Join Date: Aug 2014
Posts: 215
Received 0 Votes on 0 Posts
Missing bond? I need to somehow get the bottom off the heater to expose the wiring and check them all. I'll look for any missing casings.
 
  #4  
Old 11-04-14, 05:34 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
If this is not wired through metal conduit then for safety there should be a ground wire (bond).
 
  #5  
Old 11-04-14, 06:00 PM
Member
Thread Starter
Join Date: Aug 2014
Posts: 215
Received 0 Votes on 0 Posts
Is this the ground? In the bottom left of photo there looks like a copper wire tucked in there. Name:  image.jpg
Views: 210
Size:  29.9 KB
Name:  image.jpg
Views: 249
Size:  24.5 KB
 
  #6  
Old 11-04-14, 06:39 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Is it connected to the metal of the heater?
 
  #7  
Old 11-04-14, 06:42 PM
Member
Thread Starter
Join Date: Aug 2014
Posts: 215
Received 0 Votes on 0 Posts
One end is shown in the photo and the other end looks like it May go to a screw. I cannot tell because it's behind the metal plate over heater
 
  #8  
Old 11-04-14, 06:51 PM
dirtydickey's Avatar
Member
Join Date: Aug 2014
Posts: 54
Received 0 Votes on 0 Posts
You have been shocked already and mention having children and pets that you are concerned about. You might be better served contacting a professional rather than messing around in unchartered territory.

I trust you have the offending heater turned off at the breaker until this can be rectified?
 
  #9  
Old 11-04-14, 06:54 PM
Member
Thread Starter
Join Date: Aug 2014
Posts: 215
Received 0 Votes on 0 Posts
If it was something easy to fix I was going to myself. Yes it's turned off at the breaker
 
  #10  
Old 11-04-14, 07:25 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,088
Received 29 Votes on 23 Posts
It might be easier to start by going to the main service panel and see if the circuits are wired with a grounding conductor. If this house was built in the '50s or '60s, it's entirely possible this house was wired with the old 2-wire NM cable and that none of the circuits have a grounding conductor.
 
  #11  
Old 11-04-14, 07:36 PM
Member
Thread Starter
Join Date: Aug 2014
Posts: 215
Received 0 Votes on 0 Posts
It was built in 56'. The box has a bunch of grounds to it.
 
  #12  
Old 11-04-14, 09:33 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,505
Received 401 Votes on 377 Posts
It's not a static electricity shock..... is it ?

Even if the case of that heater was live...... unless you were touching it AND something grounded you would not get a shock.
 
  #13  
Old 11-05-14, 07:47 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
You could try to test dead resistance between the case and the heating element(s) leads to see if there's a short to the case. That would at least prove the heater as the source of the shock. If I was checking it out, I would also power the thing on, glove up and try to find some energized surfaces with my multimeter as I wiggled the thing around. But unless you've got a pair of voltage rated gloves I really don't think you should try that.

Honestly though if you called me out to look at this I don't think I would attempt a repair in good conscience knowing you've already gotten a zap from it and there's a kid in the house. If we're able to narrow down that the heater is the problem, my recommendation would be to just replace it.

Out of curiosity, what kind of flooring do you have in this room?
 
  #14  
Old 11-05-14, 04:40 PM
Member
Thread Starter
Join Date: Aug 2014
Posts: 215
Received 0 Votes on 0 Posts
Hardwood flooring. I've never been shocked from house wiring before so not sure if it was the heater or static shock.
 
  #15  
Old 11-05-14, 04:57 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,955
Received 33 Votes on 28 Posts
I think that copper under the heater fins was part of the thermostat, not a ground wire.
 
  #16  
Old 11-05-14, 08:11 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,088
Received 29 Votes on 23 Posts
I've never been shocked from house wiring before so not sure if it was the heater or static shock.
The way to find out is with a meter. A static shock is momentary and hits once, but an electrical shock should be continuous. I doubt it's a static shock or you would be getting it off other objects too.....and you have hardwood floors.
 
  #17  
Old 11-06-14, 01:04 AM
Member
Thread Starter
Join Date: Aug 2014
Posts: 215
Received 0 Votes on 0 Posts
I've gotten shocked multiple times but it hit and was gone. I'll test resistance with the ohm setting on multimeter tomorrow. Hate to even mess with it with breaker back on.
 
  #18  
Old 11-06-14, 05:57 AM
dirtydickey's Avatar
Member
Join Date: Aug 2014
Posts: 54
Received 0 Votes on 0 Posts
I'll test resistance with the ohm setting on multimeter tomorrow. Hate to even mess with it with breaker back on.

You don't test resistance in that way.
 
  #19  
Old 11-06-14, 07:15 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
As mentioned earlier wood does not conduct electricity so how could you get a shock? Checking resistance with breaker off will serve no purpose. To test:
  • Turn the heater on.
  • Plug an extension cord with a ground into a receptacle with a known good ground.
  • With a multimeter set to voltage measure from a point on the heaters metal case with no paint to the ground on the extension cord.
If you have a wall mounted thermostat with metal case preform the same test plus checking for voltage between bare metal on the thermostat and bare metal on the heater. Name:  Triangle.gif
Views: 129
Size:  1.1 KBIf you are uncomfortable doing this call an electrician.
 

Last edited by ray2047; 11-06-14 at 07:42 AM.
  #20  
Old 11-06-14, 12:28 PM
Member
Thread Starter
Join Date: Aug 2014
Posts: 215
Received 0 Votes on 0 Posts
I checked from the ground prong on an outlet to the heaters case. The painted parts I couldn't get a voltage reading but on the underside of the case and a few other spots I got up to 50 V AC.
 
  #21  
Old 11-06-14, 12:35 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Was it a digital multimeter? If so you may want to try with an analog multimeter. (A cheap $8-$15 one is fine.) On the receptacle you used for the test what is your readings ground to wide slot and ground to narrow slot.
 
  #22  
Old 11-06-14, 01:37 PM
Member
Thread Starter
Join Date: Aug 2014
Posts: 215
Received 0 Votes on 0 Posts
I have an analog multimeter. My reading from ground to wide slot is 0 V and my readings from ground to narrow slot is 120 V.
 
  #23  
Old 11-06-14, 01:52 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Then you do appear to have some leakage from the heater. That is enough to be dangerous. I'd suggest replacing the heater.
 
  #24  
Old 11-06-14, 02:28 PM
Member
Thread Starter
Join Date: Aug 2014
Posts: 215
Received 0 Votes on 0 Posts
When I held the multimeter to heater casing, should it have read 0 no matter where I touch on that casing or heating element?

When you say leakage, what do you mean?
 
  #25  
Old 11-06-14, 02:47 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
The heater casing should always measure very close to 0 volts to any reference ground. Your 50VAC measurement indicates two things: 1) some of the electrical insulating materials are breaking down and allowing energized components to contact the case, thus energizing the case. The heating element itself could have a crack in it. 2) The heater case is not adequately grounded. Neither of these is a good thing.
 
  #26  
Old 11-06-14, 02:50 PM
Member
Thread Starter
Join Date: Aug 2014
Posts: 215
Received 0 Votes on 0 Posts
The heater itself is probably 50+ years old if I had to guess as well.. Things could very well be bad
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: