unusual readings on AC circuit

Reply

  #1  
Old 11-05-14, 01:26 PM
Member
Thread Starter
Join Date: Nov 2014
Posts: 1
unusual readings on AC circuit

I have a kitchen circuit with a GFCI outlet that feeds 2 other outlets. The load line coming in reads Hot/Gnd reversed with a plug in tester. I isolated the line coming in and read 119vac (hot to gnd) but only 60vac hot to neutral. What could cause this?
 
Sponsored Links
  #2  
Old 11-05-14, 01:31 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,399
Most likely is a loss of the neutral. Hot-ground reversal on a plug-in tester usually means a lost neutral.
 