Computing amps (220v 3 phase) from 250 amp, 400 v equipment

Computing amps (220v 3 phase) from 250 amp, 400 v equipment


  #1  
Old 11-14-14, 11:04 AM
O
Member
Thread Starter
Join Date: Nov 2014
Location: usa
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Computing amps (220v 3 phase) from 250 amp, 400 v equipment

Hello, first time poster here. I have a quick question regarding converting from European voltage to US voltage.

The equipment is wired for 250 amp 400 volt service. I need to know how many amps that would pull after using a transformer to step it down to 220v 3 Phase.

If I use the general equation Watts = Volts X Amps I get 100,000 watts. If I plug that number into the equation using 220v I get 454.5 amps (100,000/220 = amps), which seems like far too much.

Is there a different equation for this conversion?


Thanks in advance
 
  #2  
Old 11-14-14, 11:12 AM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
Yes, there are different equations used with three-phase. I don't often work with three-phase so I have to look it up every time but it involves multipliers which include the following numbers. 1.41, 0.707 and 1.73 I honestly don't remember which you use or where you use it. It also depends upon the transformer connection you use.

One of the commercial electricians should be able to answer the question but it could be a few hours to even a couple of days for them to respond.
 
  #3  
Old 11-14-14, 01:17 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
So the scenario is you want to operate the equipment at 400V 3P from a 220V 3P (odd) service, using a transformer?
 
  #4  
Old 11-14-14, 04:29 PM
Mr.Awesome's Avatar
Member
Join Date: Oct 2013
Location: Canada
Posts: 511
Received 0 Upvotes on 0 Posts
What kind of equipment is this?
If it was designed to run at 400V, you may not be able to successfully use it at 220V.
And if you're talking 3 phase, you will likely be looking at running it at 208V.
 
  #5  
Old 11-14-14, 04:43 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Sounds like European equipment. UK voltage 415VAC + 6% and - 10% and European is 380VAC +10% and -6%
 
  #6  
Old 11-14-14, 07:13 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,871
Received 185 Upvotes on 166 Posts
There are too many things to remember already so I don't worry about trying to remember formulas. I just use this site to select the formula I need.

Reliance - Formulas & Calculations
 
  #7  
Old 11-14-14, 07:58 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,951 Upvotes on 3,544 Posts
Lots of useful formulas there.... thanks Joe.
 
  #8  
Old 11-14-14, 08:25 PM
Mr.Awesome's Avatar
Member
Join Date: Oct 2013
Location: Canada
Posts: 511
Received 0 Upvotes on 0 Posts
Joe,
I think the formula the OP is thinking of is for output voltage when wiring in delta and wye configurations.
 
 