Does someone know the code number on no longer using THHN in conduit outside and the year it was changed? When I've written that in the past I just went by what was written here but I have been asked for more info.
#2
Article 310
Ray, check out article 310 in the 2014 NEC, I can't remember the last time we have used THWN.
Geo
Geo
#7
Not sure if this helps. It's from the 2014 NEC.
300.9 Raceways in Wet Locations Abovegrade
Where raceways are installed in wet locations abovegrade, the interior of these raceways shall be considered to be a wet location. Insulated conductors and cables installed in raceways in wet locations abovegrade shall comply with 310.10(C).
300.9 Raceways in Wet Locations Abovegrade
Where raceways are installed in wet locations abovegrade, the interior of these raceways shall be considered to be a wet location. Insulated conductors and cables installed in raceways in wet locations abovegrade shall comply with 310.10(C).
#9
There appears to be no actual definition (article 100) for wet location,how ever underground is considered wet but conduits above grade are only considered wet if they are in areas such as dairies,carwashes etc.in which case the equipment must be set off the surface by 1/4".
Geo
Geo
#11
Of course another question is how easy is it to buy THHN. Isn't most of the wire sold marked THHN/THWN and in reality just THWN with the added specification?
#12
2014 NEC Location, Wet
Installations underground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas, and in unprotected locations exposed to the weather.
Installations underground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas, and in unprotected locations exposed to the weather.
#13
in unprotected locations exposed to the weather.
#14
Ray, I think you hit on a point. It seems Southwire is classifying their THHN and THWN-2 in the same breath. So is their THHN adaptable to wet locations? Their literature says so. Just wondering.
#19
Pretty much since the advent of full synthetic wire insulations like PVC, nylon and polyethylene there is not a whole lot of difference between the types of wire out there. I have recently seen a plain "TN" (no HH, no W) ground wire which a low voltage contractor was using as a bonding conductor between various equipment. The shade of green was unusual it caught my eye so I looked more closely -- I assume just some cheap imported wire they bought online somewhere. Anything you get from a reputable source will likely carry several ratings.