THHN In Conduit Outside

Reply

  #1  
Old 11-18-14, 10:06 AM
ray2047's Avatar
Group Moderator
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 33,044
THHN In Conduit Outside

Does someone know the code number on no longer using THHN in conduit outside and the year it was changed? When I've written that in the past I just went by what was written here but I have been asked for more info.
 
Sponsored Links
  #2  
Old 11-18-14, 11:00 AM
Member
Join Date: Nov 2012
Location: USA
Posts: 3,314
Article 310

Ray, check out article 310 in the 2014 NEC, I can't remember the last time we have used THWN.
Geo
 
  #3  
Old 11-18-14, 11:05 AM
ray2047's Avatar
Group Moderator
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 33,044
I see. Thank you for the correction. You are saying conduit outside but not underground is not a wet location.
 

Last edited by ray2047; 11-18-14 at 11:28 AM.
  #4  
Old 11-18-14, 07:07 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,385
If outside conduit would not be considered a wet location, but a dry location, NM-B cable could be used outside in conduit, right? I don't have a copy of the 2014 NEC.
 
  #5  
Old 11-18-14, 07:36 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,587
Without checking I believe it says outdoors and underground is a wet area.
 
  #6  
Old 11-18-14, 07:48 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,385
I think PCboss is correct, but if there is a change in the 2014 NEC it's possible that outdoor conduit MIGHT be just a damp location where underground conduit would be a wet location.
 
  #7  
Old 11-19-14, 04:09 PM
Member
Join Date: Sep 2009
Location: USA
Posts: 487
Not sure if this helps. It's from the 2014 NEC.

300.9 Raceways in Wet Locations Abovegrade

Where raceways are installed in wet locations abovegrade, the interior of these raceways shall be considered to be a wet location. Insulated conductors and cables installed in raceways in wet locations abovegrade shall comply with 310.10(C).
 
  #8  
Old 11-19-14, 04:32 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,587
The article just posted would rule out NM and THHN outside.
 
  #9  
Old 11-19-14, 06:14 PM
Member
Join Date: Nov 2012
Location: USA
Posts: 3,314
There appears to be no actual definition (article 100) for wet location,how ever underground is considered wet but conduits above grade are only considered wet if they are in areas such as dairies,carwashes etc.in which case the equipment must be set off the surface by 1/4".
Geo
 
  #10  
Old 11-19-14, 06:41 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,587
Article 100 has a definition for Location, Wet.
 
  #11  
Old 11-19-14, 07:15 PM
ray2047's Avatar
Group Moderator
Thread Starter
Join Date: Mar 2006
Location: USA
Posts: 33,044
Of course another question is how easy is it to buy THHN. Isn't most of the wire sold marked THHN/THWN and in reality just THWN with the added specification?
 
  #12  
Old 11-19-14, 07:28 PM
Member
Join Date: Sep 2009
Location: USA
Posts: 487
2014 NEC Location, Wet
Installations underground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas, and in unprotected locations exposed to the weather.
 
  #13  
Old 11-19-14, 09:35 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,385
in unprotected locations exposed to the weather.
That makes sense, such as under a roof, but outside. A good example would be under a roof at a loading dock, but still outside. That area would be a damp location and NM cable would still not be allowed even in conduit.
 
  #14  
Old 11-20-14, 04:07 AM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,968
Ray, I think you hit on a point. It seems Southwire is classifying their THHN and THWN-2 in the same breath. So is their THHN adaptable to wet locations? Their literature says so. Just wondering.
 
  #15  
Old 11-20-14, 04:17 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,587
The wiring is probably dual rated for both categories.
 
  #16  
Old 11-20-14, 07:51 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,385
The wiring is probably dual rated for both categories.
I cannot recall seeing any THHN that wasn't dual rated as THWN.
 
  #17  
Old 11-21-14, 08:41 AM
Member
Join Date: Nov 2012
Location: USA
Posts: 3,314
How about these ratings? THHN ,THWN ,MTW ,AWM. Same conductor.
Name:  image.jpg
Views: 1131
Size:  35.5 KB
Geo
 
  #18  
Old 11-21-14, 09:00 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,587
Pretty common, it has all the properties to meet all those categories.
 
  #19  
Old 11-21-14, 10:04 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,502
Pretty much since the advent of full synthetic wire insulations like PVC, nylon and polyethylene there is not a whole lot of difference between the types of wire out there. I have recently seen a plain "TN" (no HH, no W) ground wire which a low voltage contractor was using as a bonding conductor between various equipment. The shade of green was unusual it caught my eye so I looked more closely -- I assume just some cheap imported wire they bought online somewhere. Anything you get from a reputable source will likely carry several ratings.
 