Is there such thing as a Main Service Disconnect?
#1
Member
Thread Starter
Is there such thing as a Main Service Disconnect?
I want to replace our main breaker box that's inside the garage with some kind of disconnect switch/box but I can't seem to find one. The ideas was to replace the old main breaker box with the switch so then I could install a new main breaker box on the other side of the garage. So from the new disconnect switch there would be a SER cable (about 20 feet) going to a new main breaker box across the garage to the laundry room. But so far it looks like all i can do is install a new breaker box where the old one is, then add 100 amp breaker to it and run the cable to the new box from the 100 amp breaker and setup the other new breaker box as a subpanel.
#2
Disconnect enclosures and breakers should be at any decent electrical supply house and some big box stores.
#3
You will want something like so...
Square D by Schneider Electric 100 Amp 240-Volt Two-Pole Indoor General Duty Fusible Safety Switch with Neutral-D223N at The Home Depot
Square D by Schneider Electric 100 Amp 240-Volt Two-Pole Indoor General Duty Fusible Safety Switch with Neutral-D223N at The Home Depot
#4
Member
Thread Starter
Thanks! I swear I went through every disconnect switch page on home depot website n didn't see that one.. just 30,40, 60 amp ones.
#5
Member
Thread Starter
You will want something like so...
Square D by Schneider Electric 100 Amp 240-Volt Two-Pole Indoor General Duty Fusible Safety Switch with Neutral-D223N at The Home Depot
Square D by Schneider Electric 100 Amp 240-Volt Two-Pole Indoor General Duty Fusible Safety Switch with Neutral-D223N at The Home Depot
#7
It would still be your main.
You would be looking at meter > disconnect > panel.
Out of curiosity, why have you decided to move the panel? That seems like a ton of effort to extend all the existing circuits.
You would be looking at meter > disconnect > panel.
Out of curiosity, why have you decided to move the panel? That seems like a ton of effort to extend all the existing circuits.
#8
Member
Thread Starter
I have a very werid/old main breaker box on one side of the garage by the meter. It doesn't have a main disconnect, just about 8 breakers for different things (so there is no way to turn off all electricity to the house on 1 flip). From this main breaker box another sub panel was installed across the garage for more stuff in the house. So I want to combine both into 1 newer box. All the cables from the main breaker box can be routed to where the supanel is since the cables are long, so I would be able to make this the new location for the main breaker box (its in the laundry room). But to eliminate the subpanel and leave the main breaker box where it is I would have to put a junction box since the cables won't reach the main breaker box from the subpanel. Hopefully that makes sense 
I'm redoing the garage to make it a room. All the drywall is out so its easy to work with the boxes.
Our local Home Depot doesn't' have that disconnect you linked so I could go see it but I'm guessing its a disconnect for all 4 wires of the SER cable i'll be running across the room right?

I'm redoing the garage to make it a room. All the drywall is out so its easy to work with the boxes.
Our local Home Depot doesn't' have that disconnect you linked so I could go see it but I'm guessing its a disconnect for all 4 wires of the SER cable i'll be running across the room right?
#10
Our local Home Depot doesn't' have that disconnect you linked so I could go see it but I'm guessing its a disconnect for all 4 wires of the SER cable i'll be running across the room right?
This switch is suitable for use as service entrance equipment when equipped with a service grounding kit.
•Service entrance rate- purchase separately service ground Kit GTK0610
#11
Member
Thread Starter
Can you post a picture of the outside panel and meter?
Another strange thing i just saw is that from the electric company there are are only 3 cables, the 2 hot #2awg copper lines and a white neutral, but there is no main ground wire. I thought there had to be one main ground wire going to a ground rod or connected to something. Currently there is just a ground bar and a neutral bar in the box with all the ground wires going to them.
#12
Member
Thread Starter
The 40 amp breaker controls the other subpanel. The 30 amp breakers are for the dryer and for an oven. and the other 15 and 20 amp breakers are for lights and outlets. So no main disconnect/breaker in this box.
#13
Many power companies will not allow grounding in the meter socket. If this is the case your grounding and bonding will be in your first means of disconnect.
#14
From the power company there is only supposed to be 3 wires, Hot, hot, and the grounded conductor (neutral). The meter socket is bonded to the neutral and that is your ground. At the main disconnect the panel steel is also bonded to the neutral, as is all of the ground wires of the branch circuits. In all other sub panels the ground and neutrals are kept separate.
#15
Depending on the age of your service, you should have one or two grounding electrode conductors terminated on the neutral bus in your main panel. One should go to a ground rod and the other should go to the metallic cold water piping within 5 feet of where it enters the house.
#16
Member
Thread Starter
Depending on the age of your service, you should have one or two grounding electrode conductors terminated on the neutral bus in your main panel. One should go to a ground rod and the other should go to the metallic cold water piping within 5 feet of where it enters the house.
#17
There needs to be some sort of a grounding system. It does not matter that the water lines are not close to the meter. If the pipe is metallic and in contact with the earth for 10' or more it must be used. It would also need a supplemental electrode like a rod.
#18
Member
Thread Starter
Well that sucks, now I have to pay for rod to get installed. Our house was build in the 70's, you would think it would have something. The closest water line is about 25 feet away. And unfortunately our driveway and around the perimeter of the house is all concrete so im not sure how they will install 2 ground rods and bond them together and then to the main panel. The only way is to have them demo a large part of concrete and then repour new concrete to hide the copper wire connecting the 2 rods

#21
Since your service is original to the house it would likely be grandfathered in. I am not sure when bonding the water service to the electrical service came in, but the ground rod requirement has only been in 20 years-ish.
To drive a ground rod outside, drill a hole through the slab with a hammer drill.
To drive a ground rod outside, drill a hole through the slab with a hammer drill.
#22
Since your service is original to the house it would likely be grandfathered in. I am not sure when bonding the water service to the electrical service came in, but the ground rod requirement has only been in 20 years-ish.
#23
Member
Thread Starter
That would make sense, it was build in 1971. I'm going to try to get some prices on putting in ground rods but if its to expensive I guess I'll just connect it to the water pipe.
I was gonna try to do the ground rod myself but the slab outside is like 6+ inches thick so I would have to buy a 10' rod and I can't see how I can clear that long rod because of the house soffits, no room to hammer it down even with tool. Inside the garage is the same issue, would hit top ceiling and no room to hammer it down
I was gonna try to do the ground rod myself but the slab outside is like 6+ inches thick so I would have to buy a 10' rod and I can't see how I can clear that long rod because of the house soffits, no room to hammer it down even with tool. Inside the garage is the same issue, would hit top ceiling and no room to hammer it down
#24
I can't see how I can clear that long rod because of the house soffits,
#25
Member
Thread Starter
I can do that 
I going to drive 2 of these 6 feet apart, can the conductor joining them together be above ground or does it have to be under ground also. If has to be underground can I just cut at a line in the concrete in between the 2 ground rods just deep enough to hide the conductor wire and then cover it with cement? or does it have to be all the way to the ground under all the concrete?

I going to drive 2 of these 6 feet apart, can the conductor joining them together be above ground or does it have to be under ground also. If has to be underground can I just cut at a line in the concrete in between the 2 ground rods just deep enough to hide the conductor wire and then cover it with cement? or does it have to be all the way to the ground under all the concrete?
#26
That would make sense, it was build in 1971. I'm going to try to get some prices on putting in ground rods but if its to expensive I guess I'll just connect it to the water pipe.
#27
Member
Thread Starter
They require 2 rods, but I found a good spot to install them, there a little far (about 30 feet away) but there is no code on how far they should be. Code requires #6 CU but I'm wondering if I should use #4, or is that overkill?
Also since the subpanel is within 5 feet of the water lines, can I connect the ground bar on the subpanel to the water pipe? (ground and neutral wont be together in the subpanel just in the main panel)
Also since the subpanel is within 5 feet of the water lines, can I connect the ground bar on the subpanel to the water pipe? (ground and neutral wont be together in the subpanel just in the main panel)
#28
Also since the subpanel is within 5 feet of the water lines, can I connect the ground bar on the subpanel to the water pipe?