GFCI feeding non gfci receptacle up to code

Im installing a recep in my sink base cabinet for the dishwasher and disposal to hookup to. I recently installed a double gang box with 2 gfci's above my counter top. If I feed the receps under the sink off of the load side of the gfci, would that satisfy the requirement for the receps under the sink? Or are they all required to be an actual gfci recep?
 
  #2  
Old 11-22-14, 03:11 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,970
Received 194 Upvotes on 170 Posts
The receptacles for the countertop cannot feed under the counter appliances. You you a separate circuit for them.
 
  #3  
Old 11-22-14, 06:35 PM
C
Member
Thread Starter
Join Date: Sep 2014
Location: USA
Posts: 27
Received 0 Upvotes on 0 Posts
Alright thanks, good thing I happen to have an extra circuit already above the kitchen thats not in use yet
 
  #4  
Old 11-22-14, 07:57 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,870
Received 185 Upvotes on 166 Posts
If I feed the receps under the sink off of the load side of the gfci, would that satisfy the requirement for the receps under the sink? Or are they all required to be an actual gfci recep?
The GFCI protection can come from an upstream GFCI device or a GFCI circuit breaker. In your case, like PCboss said, you need a new circuit.
 
 