Bath vent heater switch 15A or 20A

Hello,

I have a Panasonic FV-11VH2 bath vent/heater combo. I want to use a switch that is lit when the heater is on and off when the heater is off so its really noticeable to my wife/kids since leaving it on would cost $$$. I have such a Leviton lighted 15A switch (cost like $12) but the heater instructions call for 20A circuit (I have 20AMP breaker and 12 gauge wiring). I want to know if it would be ok to use a 15A switch with 20A wiring for this purpose because the 20A lighted switch costs like $40.

From the instructions: "The heater for this unit is a 1400 W sheathed heater. A thermostat and thermal cut-off switch have been added for safety in case of an abnormal temperature rise in the heater"

Thanks.
 
Sponsored Links
  #2  
Old 11-23-14, 11:27 AM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,967
Received 6 Votes on 6 Posts
Check the functioning of the lighted switch. Most are illuminated with the switch "off", so you may still not have what you need. Leviton 15 Amp Combination Switch with 25-Watt Neon Pilot Light - White-R52-05226-0WS at The Home Depot comes on with the switch in the "on" position. You will need to find a 20 amp version. What is the amperage of the heater from the nameplate?
 
  #3  
Old 11-23-14, 12:05 PM
I
Member
Thread Starter
Join Date: Mar 2012
Location: USA
Posts: 305
Received 0 Votes on 0 Posts
The switch I already have is a 15A pilot light. I've used them before.

The nameplate says 11.9A for the heat and .3A for the vent.
 
  #4  
Old 11-23-14, 01:04 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,069
Received 1,109 Votes on 1,029 Posts
The 15A switch should be fine for that heater.
 
  #5  
Old 11-23-14, 01:31 PM
I
Member
Thread Starter
Join Date: Mar 2012
Location: USA
Posts: 305
Received 0 Votes on 0 Posts
Great thanks!

Do you know why they would require a 20A circuit though? Is that taking into account if you use the heater vent and lights simultaneously on the same circuit? Mine is the non light model.
 
  #6  
Old 11-24-14, 08:47 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,101
Received 80 Votes on 74 Posts
If the switched part of the circuit serves only the heater (perhaps with a built in light) drawing a total of 1440 watts or less then a 15 amp switch will do. (Beware of cheaper 7 amp switches that might be available but intended for lights only subcircuits.)

For a switched subcircuit that serves the heater and also has several other light fixtures or some receptacles, you would need a 20 amp switch if the overall circuit is 20 amps 12 gauge.
 
  #7  
Old 11-24-14, 08:57 AM
I
Member
Thread Starter
Join Date: Mar 2012
Location: USA
Posts: 305
Received 0 Votes on 0 Posts
I have a beefy Leviton pilot light and plan to only put the heater and nothing else on that switch.

Does the wiring still need to remain 12 gauge on that switched circuit between the switch and the heater?

I am curious because the same 20A circuit supplies power to the lights (on a different switch) and its a pain in the behind to use 12 gauge wiring for the can lights.
 
  #8  
Old 11-24-14, 09:01 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 43 Votes on 41 Posts
My guess is that if you run all the components at once it exceeds 80% of a 15A circuit, which is the limit for a continuous load on a circuit. It is somewhat debatable if this is a continuous load, but it could be accidentally left on all day and therefore meet the definition of continuous (>3 hours). There is a also a very similar code, worded slightly differently, for built-in electrical space heaters, which this unit might qualify for, that also imposes an 80% capacity limit on the circuit. The manufacturer is probably leaning on the safe rather than sorry side.

Yes all of the wiring on the 20A circuit needs to be #12. The switch needs to be sized for the load it directly controls, so you could have a few 15A switches on a 20A circuit.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: