One Romex
There is a duplex receptacle under the sink. The top receptacle is hot and is used for the dishwasher. The bottom receptacle is switched and is used for the garbage disposer. There is one 12/3 with ground going to the receptacle. In the breaker box the black goes to a 20 amp breaker for the dishwasher. The red goes to an adjacent 20 amp breaker for the disposer. The white goes to neutral. The bare goes to ground. Is it OK for these two adjacent breakers to share a neutral?
#4
Member
Thread Starter
Join Date: Nov 2014
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
They are not tied together. I will go get a handle tie and fix it.
If I convert the breakers to duel afci/gfci breakers, do I just have the neutral go to the first breaker and then jump between the neutral connections of the two breakers?
If I convert the breakers to duel afci/gfci breakers, do I just have the neutral go to the first breaker and then jump between the neutral connections of the two breakers?
#5
Member
With GFCI and a MWBC you need a two pole breaker. There are none currently made that also do AFCI the way you need for the 2014 NEC.
What brand panel do you have?
One option is to put AFCI breakers in and then change to two GFCI receptacles. Other option is to add a sub-panel for the extra breakers.
What brand panel do you have?
One option is to put AFCI breakers in and then change to two GFCI receptacles. Other option is to add a sub-panel for the extra breakers.
#6
Member
Thread Starter
Join Date: Nov 2014
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Square D Homeline. Does the 2014 code require the garbage disposer circuit to be AFCI protected? If I use two Dual Function AFCI/GFCI breakers and tie them together with a handle tie and split the neutral and have it go to each breaker will it work and will it meet code?
#8
Member
You can not tie two GFCI or AFCI/GFCI dual function breakers together.
Per Square-D - http://download.schneider-electric.c...e=HRB86114.pdf
One last option - check amperage ratings of dishwasher and GD. If low enough combine them on one 20 amp circuit and don't use the red wire in the existing 12/3 cable.
Per Square-D - http://download.schneider-electric.c...e=HRB86114.pdf
"This arc-fault and ground-fault detection device is
not designed or intended for use on circuits in
which the neutral conductor is shared with other
circuits. The circuit breaker will nuisance trip in
“shared neutral” circuits."
2014 NEC says all 120v 15 and 20 amp kitchen circuits need AFCI protection.not designed or intended for use on circuits in
which the neutral conductor is shared with other
circuits. The circuit breaker will nuisance trip in
“shared neutral” circuits."
One last option - check amperage ratings of dishwasher and GD. If low enough combine them on one 20 amp circuit and don't use the red wire in the existing 12/3 cable.
Last edited by Astuff; 11-28-14 at 02:32 PM.
#10
You have a multi-wire circuit. If this is an existing installation it would be grandfathered in. Handle ties were required about 2002, GFCI protection in 2014, and AFCI may not be required at all depending on a few things.
BTW - There are AFCI/GFCI combo single pole breakers available now.
BTW - There are AFCI/GFCI combo single pole breakers available now.
#11
BTW - There are AFCI/GFCI combo single pole breakers available now.
Are the handles tied together? They must both trip at the same time. It is called a MWBC, or multi wire branch circuit.
#12
Member
Thread Starter
Join Date: Nov 2014
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I have installed a handle tie to tie the two existing breakers together. I plan on adding a couple of circuits in the future. If I am required to bring things up to 2014 code when I do the job, I will combine the dishwasher and garbage disposer onto one circuit. If by then there is a breaker solution where I can have two circuits, then I will probably do that.
I am in Colorado. Colorado has adopted the 2014 code. When I add the two circuits I will first contact the inspector to be sure that all the old stuff is grandfathered.
Thanks a lot for the help.
I am in Colorado. Colorado has adopted the 2014 code. When I add the two circuits I will first contact the inspector to be sure that all the old stuff is grandfathered.
Thanks a lot for the help.
#13
I will combine the dishwasher and garbage disposer onto one circuit
Right now you have Disposal and Dishwasher on two circuits, that's not a bad thing. Codes change, but that doesn't mean you have to go through the house and start rewiring everything.
If safety is paramount to you, than yes, go for it. But don't feel this must be done.