UF-B Cable question

I understand that if you run cable down through the spaces of concrete block you should use UF-B because of damp conditions. I was wondering about a cable running down a wood stud exterior wall that ultimately serves an exterior outlet? Does the code indicate UF-B for that as well? My son bought a home built in 1987 in Orlando, FL. This outlet was surely added after the home was built. Wondering if it was done the "right" way. Thank you.
 
  #2  
Old 12-03-14, 02:15 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
NM can typically be run in the stud bay and into the back of a box mounted on the exterior of a wall. If the NM were run on the outside of the exterior it would be a code violation.
 
  #3  
Old 12-03-14, 02:16 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,607
Upvotes: 0
Received 9 Upvotes on 8 Posts
UF-B is not required in wood framed walls, even if it serves an exterior receptacle, unless that receptacle is not attached to the wall. If it runs under a patio, etc. then it would need to be in conduit or UF used.
 
 