upsize breaker for water heater?

Reply

  #1  
Old 12-04-14, 01:19 PM
Member
Thread Starter
Join Date: Dec 2014
Posts: 2
Received 0 Votes on 0 Posts
upsize breaker for water heater?

I have an electric water heater that is 240V, 5500W. Its manual recommends a 30A breaker. However, the installed breaker is only 25A. The breaker doesn't trip, but it does get mildly warm (not hot) and there is a faint crackling sound.

The water heater is wired with 10/2, maybe 25 feet of wire. Is there a reason the circuit might have been derated to 25A?

Bottom line, should I change out the breaker or am I OK with the one that is there? If I change it out, do I put in a 25A or 30A breaker?
 
Sponsored Links
  #2  
Old 12-04-14, 02:00 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
The breaker should be 30A. Crackling sound or buzzing?

Maybe the former water heater was a smaller unit requiring the 25A?
 
  #3  
Old 12-04-14, 02:01 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
It is best to follow the manufacturer's instruction. #10 is okay for a 30 amp circuit so go ahead and change to 30 amps. As to why it is 25, maybe that was what was on the truck of who ever did the electrical or maybe it was installed for a 4500 watt WH.
 
  #4  
Old 12-04-14, 02:19 PM
Member
Thread Starter
Join Date: Dec 2014
Posts: 2
Received 0 Votes on 0 Posts
Thanks for the replies. WH was replaced by previous owner, but they said it was an upgrade (40 gal to 50) so I would guess the old WH was lower wattage.

I think "crackling" is more accurate than "buzzing" but not sure. It's pretty faint... though I can hear it with the panel door shut but not if I'm more than 10 feet away or so.
 
  #5  
Old 12-04-14, 02:52 PM
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,489
Received 32 Votes on 24 Posts
National Electrical Code mandates that residential storage tank water heaters be served by a branch circuit calculated at 125% of the load. For a 5500 watt heater that would be 28.65 amperes. Your currently installed 25 ampere circuit breaker does not meet code and should be replaced with a 30 ampere CB.
 
  #6  
Old 12-05-14, 10:42 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,943
Received 30 Votes on 26 Posts
The noise may be caused by a loose connection to the bus bars. I would check before the bars are ruined. It could also lead to a fire.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: