50 Amp Feed to Heatpump

I am reinstalling a heat pump. The heat pump has three field connections, red and black 240 vac and a green ground wire. The feed breaker is 50 amps.
It will connect to a sub panel that is fed from a 200 amp main.
I plan to run a 6 awg red and black from the breaker in the subpanel to a 60 amp non fused safety disconnect. The red and black will then run to the heat pump.
Question 1:
Do I run a green from the subpanel ground bus to the disconnect? I assume the neutral bar is separate in the subpanel and I will not use it.
Question2:
Can I use 10 awg for the green ground wire? I am using 6 awg for the red and black. I do have some white 8 awg but I think I need to use some green tape on it to identify it as a ground.
 
Sponsored Links
  #2  
Old 12-06-14, 03:30 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,941
Received 30 Votes on 26 Posts
What are the minimum circuit ampacity needed? It will differ from the maximum breaker size. You can find this on the data plate on the unit.
 
  #3  
Old 12-06-14, 04:13 PM
n1ml's Avatar
Member
Thread Starter
Join Date: Feb 2006
Location: South Florida
Posts: 452
Received 0 Votes on 0 Posts
The minimum ampacity is listed at 40 amps. The maximum breaker size is 60 amps.
 
  #4  
Old 12-06-14, 04:18 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,941
Received 30 Votes on 26 Posts
You only need #8, but can run the #6 if you want.
 
  #5  
Old 12-06-14, 05:57 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,042
Received 26 Votes on 20 Posts
Can I use 10 awg for the green ground wire?
#10 is fine for the ground. What is the tonnage of that heat pump? I am guessing it's a big one and perhaps as big as 5 to 7 1/2 tons (probably closer to 7 1/2). I haven't seen a 5 ton unit with a 40 amp MCA in over 30 years.
 
  #6  
Old 12-06-14, 06:07 PM
n1ml's Avatar
Member
Thread Starter
Join Date: Feb 2006
Location: South Florida
Posts: 452
Received 0 Votes on 0 Posts
It is 8 1/3 ton, 100,000 BTUs.
 
  #7  
Old 12-06-14, 06:12 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,042
Received 26 Votes on 20 Posts
I knew it must be a big one.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: