FMC vs AC/BX
#1
Member
Thread Starter
Join Date: Nov 2010
Location: USA
Posts: 302
Upvotes: 0
Received 0 Upvotes
on
0 Posts
FMC vs AC/BX
Can someone tell me if there is a difference in terms of code between Flexible Metal Conduit and Armoured Cable? I've got a very short run (about 2') of AC and I like the idea of an FMC rather than AC as it'll be easier to cut. It's just a run of 14\2.
Thanks!
Thanks!
#2
No differences for code, just different wiring methods with different rules to follow. If you want to use FMC, go ahead. While code does not require it for a 2' run, I would recommend pulling in a ground wire.
#5
Member
Thread Starter
Join Date: Nov 2010
Location: USA
Posts: 302
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Just looking for a simple way to guard the NM. I need to do a short run from a box to and external transformer. Transformer can't be covered, but AC needs to be protected. Easier to use the NM I already have.
#7
Member
Thread Starter
Join Date: Nov 2010
Location: USA
Posts: 302
Upvotes: 0
Received 0 Upvotes
on
0 Posts
It's not outside at all. It's a run from a wall box to an LED transformer/rectifier. It's on top of my cabinets. 120ac comes up from the basement to a wall switch. Switched 120ac up to above the cabinets where a transformer exists. Then the 12vdc back down to the leds undercabinet.
#12
Member
Thread Starter
Join Date: Nov 2010
Location: USA
Posts: 302
Upvotes: 0
Received 0 Upvotes
on
0 Posts
One place is 84" and the other is probably 90" (we have 9' ceilings).
And I did email the city inspector to see what he would consider "subject to damage" since he's the one that ultimately signs the paper :-)
And I did email the city inspector to see what he would consider "subject to damage" since he's the one that ultimately signs the paper :-)
#13
It is pretty common to poke some Romex out of the drywall on top of the cabinets to power the light transformer. I don't expect there to be any problem from the inspector on this one.
#14
Member
Thread Starter
Join Date: Nov 2010
Location: USA
Posts: 302
Upvotes: 0
Received 0 Upvotes
on
0 Posts
really? And I could get away without a junction box up there too then? Wouldn't I need some sort of strain relief to make sure the Romex doesn't get yanked or anything?