What breaker for 200A main panel going to 100A subpanel?


  #1  
Old 12-10-14, 06:07 AM
M
Member
Thread Starter
Join Date: Nov 2014
Posts: 29
Received 0 Votes on 0 Posts
What breaker for 200A main panel going to 100A subpanel?

I'm using 2-2-2-4 Aluminum MHF to power my 100A subpanel from my 200A main panel. The main panel is a Cutler Hammer but I can't find a model number.

I need a 90A double pole breaker that is certified for Al wire. Is this the one I need? Zooming in shows the Cu-Al rating, but do I really need AFCI like I see around?

Thanks
 
  #2  
Old 12-10-14, 06:22 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,942
Received 44 Votes on 42 Posts
The breaker you linked is the correct one for a Cutler-Hammer CH series panel. These are quite easy to distinguish because the other breakers will have handle colored other-than-black and the slots are 3/4" high instead of 1" high. Culter/Eaton/etc also makes some other series panels so double check before you buy.

AFCI breakers are required for branch circuits in residences. Panel feeders do not require AFCI.
 
  #3  
Old 12-10-14, 06:39 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,254
Received 114 Votes on 99 Posts
The CH classic breakers have a brown handle and the panel is brown. Their other series is BR and the panel is gray.
 
  #4  
Old 12-10-14, 06:46 AM
M
Member
Thread Starter
Join Date: Nov 2014
Posts: 29
Received 0 Votes on 0 Posts
I think my panel is different, then. All of my breakers are black handled, and although I still can't find a model number I read this on the inside of the panel:

"Use Cutler Hammer/Westinghouse type BD, BJ, BJH, BQ, BQC, BR, BRD, BRH, BRO, BRSN, GFCB, GFEP OR GFCBH circuit breakers or Challenger type A, C, CBJ, CBJH, HC or HAGF circuit breakers."

Edit

pcboss - Thanks, yes I see a lot of "BR" references on the panel. So this is in fact what I need, right? Nice to see product numbers directly relate to the product "BR290" for BR series, 2 pole, 90A rated. So considerate!
 
  #5  
Old 12-10-14, 07:20 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,942
Received 44 Votes on 42 Posts
The BR290 is the correct breaker.
 
 