Outlet issues

All my kitchen outlets do not work, my cheap meter says there is 118 V but nothing plugged in works. Any ideas? Checked the breaker box and it shows the same volts leaving the breaker. Could this be a ground issue?
 
  #2  
Old 12-12-14, 05:05 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 36,608
Upvotes: 0
Received 9 Upvotes on 8 Posts
Welcome to the forums! What type instrument are you measuring voltage with? An analog meter is best for DIY work. About $10 at the box stores. I doubt it is a grounding problem, but it could be a neutral problem. Are you measuring at a GFCI receptacle? What are you measuring between? Hot and neutral or hot and ground?
 
  #3  
Old 12-12-14, 05:12 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,894
Received 163 Upvotes on 142 Posts
The loss of a ground will not stop the circuit from working.
 
  #4  
Old 12-12-14, 09:21 PM
P
Member
Thread Starter
Join Date: Dec 2014
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Measuring ground to hot, no GFI. Would checking between the hot and neutral indicate if there is a problem?
 
  #5  
Old 12-12-14, 10:45 PM
M
Member
Join Date: Nov 2013
Location: Canada
Posts: 35
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes, you should be checking hot-to-neutral (the two blades, not the ground). Are you checking both top and bottom of your kitchen plugs? Kitchen circuits are supposed to be separated - top and bottom should be on two different circuits. If both are out, you likely have a missing neutral.

Edit: you should also read around 240V if you measure between the two hot spades.
 
  #6  
Old 12-12-14, 11:25 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
Matt..... I believe the split receptacle method is code in Canada but is not usually used here in the States.
 
  #7  
Old 12-13-14, 07:34 AM
M
Member
Join Date: Nov 2013
Location: Canada
Posts: 35
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ah, did not know that, PJ. Good to know. And still worth checking for
 
  #8  
Old 12-13-14, 08:46 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,786
Received 173 Upvotes on 156 Posts
Measuring ground to hot, no GFI. Would checking between the hot and neutral indicate if there is a problem?
Yes! If measuring hot to ground gives you 118 volts and nothing works when plugged in, you have probably lost the neutral.
 
 