Outlet issues
All my kitchen outlets do not work, my cheap meter says there is 118 V but nothing plugged in works. Any ideas? Checked the breaker box and it shows the same volts leaving the breaker. Could this be a ground issue?
#2
Welcome to the forums! What type instrument are you measuring voltage with? An analog meter is best for DIY work. About $10 at the box stores. I doubt it is a grounding problem, but it could be a neutral problem. Are you measuring at a GFCI receptacle? What are you measuring between? Hot and neutral or hot and ground?
#5
Member
Join Date: Nov 2013
Location: Canada
Posts: 35
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Yes, you should be checking hot-to-neutral (the two blades, not the ground). Are you checking both top and bottom of your kitchen plugs? Kitchen circuits are supposed to be separated - top and bottom should be on two different circuits. If both are out, you likely have a missing neutral.
Edit: you should also read around 240V if you measure between the two hot spades.
Edit: you should also read around 240V if you measure between the two hot spades.
#6
Matt..... I believe the split receptacle method is code in Canada but is not usually used here in the States.
#8
Measuring ground to hot, no GFI. Would checking between the hot and neutral indicate if there is a problem?