Sub-Panel installation question. Furnace wire to run sub panel???? maybe?

Sub-Panel installation question. Furnace wire to run sub panel???? maybe?

Reply

  #1  
Old 12-26-14, 11:07 PM
Member
Thread Starter
Join Date: Dec 2014
Posts: 1
Sub-Panel installation question. Furnace wire to run sub panel???? maybe?

I am new to electrical. I have a basic understanding but not vast. I know I need to install a sub panel for the work I will be doing in my home. The question is can I use the power line that currently runs to the furnace to supply the sub panel, then run the furnace off the sub panel. I am thinking this becasue it would be cleaner to avoid ripping down things and I want to put a sub panel next to the furnace anyway for a welder in the garage and some lighting in the basement. Also to save th cost of buying wire which I am sure is expensive.

The furnace runs off of a 90amp breaker. The wire to the furnace from the 90 amp breaker is E32071 (U L) 2-2-2 AL. TRIPLE - E ALLOY TYPE SE CABLE STYLE U TYPE XHHW CDRS 300V. TO GROUND.

This is overkill isnt it but can I do it?

The panel will supply power to

Furnace: 208/230 Volts
Dual Supply Circut
L1/L2 Heater Amps 36.2/40.0 Miin. Ampacity 53.8/58.5
max overcurrent protection 60/60
L3/L4 Heater Amps 18.1/20.0 Min. Ampacity 22.8/25.0
max overcurrent protection 25/25


Welder: 220Volt / 60 Hz / Single Phase / 24.5Amps 3-Prong, 220V AC, polarized, twist lock NEMA#L6-30


2-3 outlets in Garage and a couple on the inside of the wall inside if It is possible.
possibly a bathroom.


Any advice would be apprciated.
I can comprehend everything I have ever been told so far about electrical so I am 100% positive I can understand whatever you throw at me.

thanks!
 
Sponsored Links
  #2  
Old 12-27-14, 05:35 AM
Member
Join Date: Jun 2008
Location: VA.
Posts: 813
No, you can't use the existing cable for a sub panel.

Your existing cable is type SEU which only contains 3 wires.

You'll need type SER for a sub panel, which contains 3 insulated conductors and a bare ground.
 
  #3  
Old 12-27-14, 07:30 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,212
The furnace circuit has no neutral conductor, just 2 hots and 1 ground. It appears you have a 2 circuit 15 KW electric furnace. I am wondering how those 2 circuits are powered by one 90 amp circuit. Since your SEU cable is only rated 300 volts to ground, I am assuming this installation is from the '80s or earlier.
 
  #4  
Old 12-27-14, 08:07 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,350
In addition, the circuit for your air handler should remain dedicated.
 
  #5  
Old 12-27-14, 09:16 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 11,979
The furnace running at full tilt will draw about 83 amps. There is not any ampacity available on that circuit.
 