Advice on dedicated circuits for kitchen
#1
Member
Thread Starter
Advice on dedicated circuits for kitchen
Hello everyone,
I've read and found some info, but still need advice.
Need some advice for wiring kitchen outlets for various equipment. Here is what I plan to do, please let me know your thoughts and/or correct me. All using 12/2 nm-b.
I completed installing 9 75W recessed cans on one dedicated 20A circuit (split between 2 dimmers). Using 11W LED floods
This is what is planned non GFCI:
Dedicated 20A for dishwasher (plug wired)
Dedicated 20A for Refrigerator
Dedicated 20A for Gas range
Dedicated 20A for Range hood (plug wired)
Dedicated 20A for Garbage disposal (plug wired)
Dedicated 20A for:
1 hydronic kick space heater (.5A)
1 electronic kick space heater (8.33A) (ancillary heat--only used when hydronic kick space heater isn't blowing enough warm air)
7 GFCI small appliance counter receptacles split between two 20A (4 on one 20A, 3 on the other 20A). The load for these will comprise of:
1 Toaster over (1200W, 10A)
1 Coffee maker (1425W ,11.9A)
Maybe a stand mixer in the future
Occasionally, a phone and/or laptop charger and/or an under cabinet radio
My goal is to put the toaster oven on one and the coffee maker on the other.
We may get a second toaster oven very soon, so should I split the GFCI counter receptacles into more 20A breakers?
I can do 2 on one 20A, 2 on another 20A and 3 on the last 20A.
No island.
I also want to put two wild card outlet that is 12" off the floor by the exterior door of our kitchen and wondering if I can tie that into something else or should I run a dedicated circuit for those two outlets? I was wondering if I can tap into the garbage disposal or range or range hood for those two. These outlets will be just for whatever necessary, not small appliances like the counter top receptacles.
I'm in Philadelphia, PA.
Thanks.
I've read and found some info, but still need advice.
Need some advice for wiring kitchen outlets for various equipment. Here is what I plan to do, please let me know your thoughts and/or correct me. All using 12/2 nm-b.
I completed installing 9 75W recessed cans on one dedicated 20A circuit (split between 2 dimmers). Using 11W LED floods
This is what is planned non GFCI:
Dedicated 20A for dishwasher (plug wired)
Dedicated 20A for Refrigerator
Dedicated 20A for Gas range
Dedicated 20A for Range hood (plug wired)
Dedicated 20A for Garbage disposal (plug wired)
Dedicated 20A for:
1 hydronic kick space heater (.5A)
1 electronic kick space heater (8.33A) (ancillary heat--only used when hydronic kick space heater isn't blowing enough warm air)
7 GFCI small appliance counter receptacles split between two 20A (4 on one 20A, 3 on the other 20A). The load for these will comprise of:
1 Toaster over (1200W, 10A)
1 Coffee maker (1425W ,11.9A)
Maybe a stand mixer in the future
Occasionally, a phone and/or laptop charger and/or an under cabinet radio
My goal is to put the toaster oven on one and the coffee maker on the other.
We may get a second toaster oven very soon, so should I split the GFCI counter receptacles into more 20A breakers?
I can do 2 on one 20A, 2 on another 20A and 3 on the last 20A.
No island.
I also want to put two wild card outlet that is 12" off the floor by the exterior door of our kitchen and wondering if I can tie that into something else or should I run a dedicated circuit for those two outlets? I was wondering if I can tap into the garbage disposal or range or range hood for those two. These outlets will be just for whatever necessary, not small appliances like the counter top receptacles.
I'm in Philadelphia, PA.
Thanks.
#2
The code allows all the receptacles in the kitchen and dining areas to be on the 20 amp small appliance circuits to serve the walls and countertop areas. The gas stove can be on one of these. I would not waste a circuit for a dedicated stove. The refrigerator can also be on the countertop circuit.
I would use a 15 amp circuit for the lights and heaters, not a 20.
The DW may require gfi protection depending on enforced code cycle. It might be able to share the circuit with the disposal.
I don't see anything about a microwave. Countertop unit?
I would use a 15 amp circuit for the lights and heaters, not a 20.
The DW may require gfi protection depending on enforced code cycle. It might be able to share the circuit with the disposal.
I don't see anything about a microwave. Countertop unit?
#3
Member
Thread Starter
No microwave. We use a toaster oven as out food heating unit, other than the regular oven.
Just wondering if I have the small appliance outlets wired to the same circuit, if I use the toaster oven and coffee maker at the same time, will the breaker trip, being that the total amps are about 22A? I'm not an electrician, just going off the numbers.
I could put the stove, the two wall outlets near the exterior door on one 20A.
If I put the dishwasher and garbage disposal on the same, the amps would total 17.3. This is slightly over the 80% load maximum.
My goal in working up these numbers and electrical runs are if we max out at any given time with using any equipment, I want to be within a comfortable limit of electrical load.
I will be adding receptacles for the upstairs bedroom and adjacent dining room, but was planning to put them on a separate circuit. They would only be supplying usual electronic devices like an iron, clock radio and such..
Already ran the 12/2 for the lights and just decided to put on a 20A since the cost of a 20A and 15A is the same for me. I can switch out to a 15. What would be the benefit?
Just wondering if I have the small appliance outlets wired to the same circuit, if I use the toaster oven and coffee maker at the same time, will the breaker trip, being that the total amps are about 22A? I'm not an electrician, just going off the numbers.
I could put the stove, the two wall outlets near the exterior door on one 20A.
If I put the dishwasher and garbage disposal on the same, the amps would total 17.3. This is slightly over the 80% load maximum.
My goal in working up these numbers and electrical runs are if we max out at any given time with using any equipment, I want to be within a comfortable limit of electrical load.
I will be adding receptacles for the upstairs bedroom and adjacent dining room, but was planning to put them on a separate circuit. They would only be supplying usual electronic devices like an iron, clock radio and such..
Already ran the 12/2 for the lights and just decided to put on a 20A since the cost of a 20A and 15A is the same for me. I can switch out to a 15. What would be the benefit?
#4
The smaller wires are easier to work with and the expected load was not even close to the 15 amp.
What are the amps on the DW and GD separately?
A 2 amp overload would hold for hours before tripping. In fact a breaker can hold over 125% for two hours and still be within spec.
What are the amps on the DW and GD separately?
A 2 amp overload would hold for hours before tripping. In fact a breaker can hold over 125% for two hours and still be within spec.
#5
Member
Thread Starter
GD is 6.3A
DW is 11A.
I have the flexibility to do whatever is easiest, but most importantly, safest.
I bought 2 250ft spools of 12/2 and already started using it, so I am fine continuing with 12/2. No big deal for me.
Thanks.
DW is 11A.
I have the flexibility to do whatever is easiest, but most importantly, safest.
I bought 2 250ft spools of 12/2 and already started using it, so I am fine continuing with 12/2. No big deal for me.
Thanks.
#6
Group Moderator
From a code standpoint, you're ok. Overkill comes to mind to describe some of what you're proposing but that's not a code violation. And, if you've already bought all of the 12/2 cable you're going to need for this and are fine with the cost and hassle of it over 14/2, then go right ahead.
#7
Member
Thread Starter
Thanks.
What would be the best way to wire everything?
1 Frigde
1 gas range
1 range hood
1 dishwasher
1 Garbage disposal
7 GFCI counter small appliance outlets
2 general purpose outlets
2 kick space heaters
Only the kickspace heaters are not corded.
Thanks.
What would be the best way to wire everything?
1 Frigde
1 gas range
1 range hood
1 dishwasher
1 Garbage disposal
7 GFCI counter small appliance outlets
2 general purpose outlets
2 kick space heaters
Only the kickspace heaters are not corded.
Thanks.
#8
The general purpose wall receptacles can be on with the two countertop circuits. If you wanted you could add a third countertop circuit and feed them from this.
I would add the stove to one of the countertop circuits. The only stove load is a micro ignitor, the clock and the oven light.
Other than that I agree with your last plan.
I would add the stove to one of the countertop circuits. The only stove load is a micro ignitor, the clock and the oven light.
Other than that I agree with your last plan.
#9
Member
Thread Starter
So, basically, this is what I could do:
1 20A for the two kickspace heaters
1 20A for the DW and GD
1 20A for the refrigerator + 4 small appliance receptacles
1 20A for the 2 general purpose outlets, the other 3 small appliance receptacles and the range + range hood.
I can split the range and range hood + 2 general purpose outlets onto one, if safer.
Let's say we upgrade the range to one with a convection oven (still gas), am I still okay with the current planned load?
This okay?
Thanks.
1 20A for the two kickspace heaters
1 20A for the DW and GD
1 20A for the refrigerator + 4 small appliance receptacles
1 20A for the 2 general purpose outlets, the other 3 small appliance receptacles and the range + range hood.
I can split the range and range hood + 2 general purpose outlets onto one, if safer.
Let's say we upgrade the range to one with a convection oven (still gas), am I still okay with the current planned load?
This okay?
Thanks.
#10
If the range hood is cord and plug connected it must be on a dedicated circuit.
I would make the DW and the GD separate.
You would need to check the amps of the convection oven. If in doubt make it a dedicated circuit.
I would make the DW and the GD separate.
You would need to check the amps of the convection oven. If in doubt make it a dedicated circuit.
#11
What would be the best way to wire everything?
Gas convection ovens are usually like 1 amp load, so I don't see a problem leaving it on the countertop circuits.
I would probably do something very close to your post #9, with the exception of a dedicated 20A circuit for the range hood.
#12
Member
Thread Starter
Ok. Cool. Thanks.
Looks like the convection oven's I've looked at just mention "A 120 volt, 60 Hz., AC only, 15-amp fused electrical circuit is required." The manual did not mention Amps or watts.
Separate the Range hood, no problem.
As long as my garbage disposal and Dishwasher is fine on the same circuit, I'm good to go. This will actually save me a run because I will switch one of the duplex receptacles with 3 wire and leave the other, for the dishwasher, live.
Actually, the manual for the dishwasher states:
When preparing for installation, ensure that your power supply offers:
• A 120 Volt 60 Hz 15 AMP fuse or circuit breaker
• An individual branch circuit serving only your dishwasher
At 11 amps, can I still combine the DW with the GD or separate, per the manufacturer's instruction?
Thanks.
Looks like the convection oven's I've looked at just mention "A 120 volt, 60 Hz., AC only, 15-amp fused electrical circuit is required." The manual did not mention Amps or watts.
Separate the Range hood, no problem.
As long as my garbage disposal and Dishwasher is fine on the same circuit, I'm good to go. This will actually save me a run because I will switch one of the duplex receptacles with 3 wire and leave the other, for the dishwasher, live.
Actually, the manual for the dishwasher states:
When preparing for installation, ensure that your power supply offers:
• A 120 Volt 60 Hz 15 AMP fuse or circuit breaker
• An individual branch circuit serving only your dishwasher
At 11 amps, can I still combine the DW with the GD or separate, per the manufacturer's instruction?
Thanks.
#13
Those two bullets indicate the manufacturer requires a dedicated 15A circuit for the DW. You can use #12 wire, but it should have a 15A breaker.
#14
Member
Thread Starter
Manual for the range hood specifies:
A 120 volt, 60 Hz., AC only, 15-amp, fused
electrical circuit is required.
A 120 volt, 60 Hz., AC only, 15-amp, fused
electrical circuit is required.
#15
Member
Thread Starter
Thanks again for all the info. Not trying to beat a dead horse, but just want to be code compliant and safe.
since I added the mfg requirements, the GD is now throwing me off. Should I just do a dedeicated circuit? At some of the NEC code I've found, I can't supply power to the GD from the small appliance branch circuit.
Since I want to add 2 outlets to the dining room wall (sharing the kitchen), can I do the following:
1 15A for DW
1 15A for range hood
1 20A for refrigerator + 3 small appliance counter top outlets
1 20A for 2 general purpose outlets + range + 1 small appliance counter top outlet (if there is no load issue, I can drop this to 15A and put the one counter top on the circuit with the refrigerator in anticipation of the new convection range or leave alone)
1 20A for 3 small appliance counter outlets + 2 dining room outlets
1 20A for 2 heaters and GD
With my anticipated small appliances, any load issues with this plan?
Also, any load issues with the 2 heaters and GD on the same circuit?
Thanks.
since I added the mfg requirements, the GD is now throwing me off. Should I just do a dedeicated circuit? At some of the NEC code I've found, I can't supply power to the GD from the small appliance branch circuit.
Since I want to add 2 outlets to the dining room wall (sharing the kitchen), can I do the following:
1 15A for DW
1 15A for range hood
1 20A for refrigerator + 3 small appliance counter top outlets
1 20A for 2 general purpose outlets + range + 1 small appliance counter top outlet (if there is no load issue, I can drop this to 15A and put the one counter top on the circuit with the refrigerator in anticipation of the new convection range or leave alone)
1 20A for 3 small appliance counter outlets + 2 dining room outlets
1 20A for 2 heaters and GD
With my anticipated small appliances, any load issues with this plan?
Also, any load issues with the 2 heaters and GD on the same circuit?
Thanks.
#16
The range hood wiring needs to be #12 (NEC requires capability to upgrade to a microwave range hood). The SABCs have to be 20A, so no dropping to 15A there. I don't see any other issues.
#17
Member
Thread Starter
The range hood wiring needs to be #12
I'm trying to leave everything in a state where if an upgrade is needed, wiring will be already in place.
I'm also back to just wondering if I should run a dedicated circuit for the fridge, but I haven't gotten that far.
Thanks for all the help. The GD and two heaters were my main concern because if I had to run the electrical heater and the GD at the same time, the average amps would be at about 15. Still below the 80% threshold, but I just want to be safe.
#18
It's no problem. The 80% threshold is for continuous loads (running more than 3 hours). Intermittent loads can go to 100% of the circuit ampacity. While the heater could be a continuous load, the disposal is not.
#19
Need some advice for wiring kitchen outlets for various equipment. Here is what I plan to do, please let me know your thoughts and/or correct me. All using 12/2 nm-b.
#20
I think this project has been well covered.
I just wanted to say I have a gas convection oven, I had to add a dedicated circuit for it.
It has the fan, a heating element in the fan, and a heating element in the warming drawer. (120).
It was tripping when shared with the small appliance/counter circuit.
I just wanted to say I have a gas convection oven, I had to add a dedicated circuit for it.
It has the fan, a heating element in the fan, and a heating element in the warming drawer. (120).
It was tripping when shared with the small appliance/counter circuit.
#21
Member
Thread Starter
What version of the NEC do you have to wire to?
I've read the sections of the document available and nothing is as stringent as NEC (from what I've read about NEC).
The doc also mentions install prefabricated wire in accordance with the NEC, but that's it.
Anyone can correct me if I am wrong. Here is the link to the doc: http://www.wilberelectrical.com/down...de%20Phila.pdf
I've also found one other doc online that mentions Pennsylvania has adopted the International Building code and International Residential Code, which references 2008 NEC, but does not mention Philadelphia individually.
Thanks.
#22
Member
Thread Starter
I think this project has been well covered.
I just wanted to say I have a gas convection oven, I had to add a dedicated circuit for it.
It has the fan, a heating element in the fan, and a heating element in the warming drawer. (120).
It was tripping when shared with the small appliance/counter circuit.
I just wanted to say I have a gas convection oven, I had to add a dedicated circuit for it.
It has the fan, a heating element in the fan, and a heating element in the warming drawer. (120).
It was tripping when shared with the small appliance/counter circuit.
I ran multiple lines today, but haven't connected them.