Electrical work recommendation for a wall oven

Hi everyone, new to the forum and been reading up various threads.

Now looking for some recommendation on a new appliance in the kitchen.
We decided to use the microwave cutout for a steam oven instead.

Now here is the setup at the cabinet cutout.
-110v recep occupying single pole 15 amp breaker on a 14/2 nmd90 wire.
- Below the mircowave i have a 240v junction box with 8/3 nmd90 wire on 2pole 40amp, planned for another single wall oven using 30amp.
The steam oven reqs 240v 15amp, the single wall oven uses 30amp.

As i lookup
- a 14/2 wire can support a 240v 15 amp 2-pole break - so it should work by replacing the breaker?
- a 8/3 can support 240v 45 amp 2-pole break - since both of my appliances use 45 amp total it should work by replacing this breaker too?

Obviously i don't have the technicality to DIY and I will be hiring a electrician to do the work but would like some reference points prior to getting it done - esp given the situation i don't know which route is "better" if it works at all.

Any suggestions?

Thanks!!
 
Sponsored Links
  #2  
Old 01-14-15, 09:04 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,365
You do not want to combine the appliances into one circuit. Keep them separate as designed.

AFAIK, #14 is good for 15 amps, the same as under the NEC.
 
  #3  
Old 01-14-15, 09:14 AM
Member
Thread Starter
Join Date: Jan 2015
Location: canada
Posts: 5
Thanks for the quick response.

Just for learning... do wonder what would be the possible issue with combining 2 appliances into one circuit if there is sufficient wire/break?

Thanks!
 
  #4  
Old 01-14-15, 09:21 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,365
Most appliances call for dedicated circuits.
 
  #5  
Old 01-14-15, 06:45 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,221
a 14/2 wire can support a 240v 15 amp 2-pole break - so it should work by replacing the breaker?
Assuming you are in Canada (you didn't complete your profile), there may be a problem. I am not a CEC expert, but I do seem to remember from other threads that in Canada a red jacketed NM cable is required for 240 volt circuits. Hopefully someone else will chime in on this.
 
  #6  
Old 01-14-15, 07:38 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,508
The steam oven reqs 240v 15amp, the single wall oven uses 30amp.
Are those the amperages of the required circuits or the amperages of the appliances ?

If the steam oven is rated for 15A at 240v then it needs to be on #12 wiring for 20A.
Is the wall oven USES 30A at 240v then it needs its own 45A circuit.

Even if you were able to combine both appliances on the 8/3 circuit you would need a circuit panel in the kitchen. You couldn't put a 15A load on a 45A breaker... there would be no protection.

The OP is in Canada.
 
  #7  
Old 01-15-15, 08:36 AM
Member
Thread Starter
Join Date: Jan 2015
Location: canada
Posts: 5
thanks for the additional info.

yes this is for canada & the steam 15a/240v and wall oven 30a/240v are per appliance usages.
what the builder roughed in is 14/2 on 120v/15amp and 8/3 on 240v/40amp.

looks like this is turnning into a bigger task requiring new wiring after all.
 
  #8  
Old 01-15-15, 08:56 AM
Member
Thread Starter
Join Date: Jan 2015
Location: canada
Posts: 5
actually re-reading the steam's manual, actually it says "circuit breaker = 15amp". electrical rating 1.9 kw @ 240v - so that's approx 8amp usage?
 
  #9  
Old 01-15-15, 09:33 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,365
Your math is correct.

Why do you think new wiring is needed? The #14 should be good for 15 amps.
 
  #10  
Old 01-15-15, 11:42 AM
Member
Thread Starter
Join Date: Jan 2015
Location: canada
Posts: 5
actually that thought was in between reading the percentage load requirement and having the steam's requiring 15amp so lead to thinking i need a 20amp new circuit....which then need at least a 12awg wire..

but after revisiting the manual looks like the 15amp is good so i can drop that thoguht


p.s. sry about the double posting
 