Breaker goop?
Old 01-14-15, 06:13 PM
Breaker goop?
As I'm replacing / moving some breakers, I noticed on the back of the original ones there's this charcoal-colored goop on the contact area. Is this supposed to be there?
Old 01-14-15, 06:15 PM
pcboss's Avatar
Received 194 Upvotes on 170 Posts
That looks like the breaker has taken too much heat and melted. Compare that to a new breaker to see how it should look.
Old 01-14-15, 06:25 PM
It's not melted plastic. It's like a grease.
Old 01-14-15, 06:36 PM
Received 3,892 Upvotes on 3,489 Posts
Some electricians apply Penetrox, which is an anti corrosion grease, to aluminum bus bars in panels. Although not required and is not detrimental to the performance of the breaker.... that is way too much on those breakers. There should only be a very thin film.
If you intend to clean the bus bars be sure to turn off the main before touching them. Wouldn't hurt to check them with a meter to confirm they are dead.
Old 01-14-15, 08:19 PM
CasualJoe's Avatar
Received 185 Upvotes on 166 Posts
I also think that is anti-oxidant grease and it should have never been used. Anti-oxidant is used to protect aluminum wire connections from oxidizing. The aluminum busbars in a loadcenter/panelboard are tin plated, the anti-oxidant does nothing except make a huge friggen mess.
Old 01-14-15, 09:07 PM
Hahaha OK, thanks..........