Need a timer for 240v irrigation well
#1
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Need a timer for 240v irrigation well
Hello,
I live in Fremont County, Colorado. I am looking for help with finding a timer/relay for my 220v, 5hp, 28amp, 70gpm agricultural irrigation well. The existing control is a set of 2 -30amp circuit breakers in a Siemens A series type 3R outdoor load center. I want to be able to set the pump to run daily for 30 – 60 minutes during the growing season. Can anyone suggest a timer/relay, and/or combination, that would work for this application?
Thanks,
Matt G
I live in Fremont County, Colorado. I am looking for help with finding a timer/relay for my 220v, 5hp, 28amp, 70gpm agricultural irrigation well. The existing control is a set of 2 -30amp circuit breakers in a Siemens A series type 3R outdoor load center. I want to be able to set the pump to run daily for 30 – 60 minutes during the growing season. Can anyone suggest a timer/relay, and/or combination, that would work for this application?
Thanks,
Matt G
#2
Welcome to the forums.
You mentioned the type 3R outdoor load center..... was that for size requirements ?
You need a basic timer and a two pole motor duty contactor.
There are many choices.... will you be purchasing at an electrical supply house or online ?
You mentioned the type 3R outdoor load center..... was that for size requirements ?
You need a basic timer and a two pole motor duty contactor.
There are many choices.... will you be purchasing at an electrical supply house or online ?
#3
I use this type for my diesel engine heater. Selectable voltage. GE, 7 Day Digital Outdoor Box Timer and On/Off Per Day, 15136 at The Home Depot - Tablet
#4
Can anyone suggest a timer/relay, and/or combination, that would work for this application?
#5
How is the pump controlled now,you must already have some sort of Contactor to control a 5 HP pump.
Geo
Geo
#6
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks for the responses
The pump is controlled by a pair of 30 amp circuit breakers in a type 3r outdoor load center which was in place when I purchased the property. I was hoping someone could recommend a specific model/part number of timer and contactor that I could buy online.
#7
I was hoping someone could recommend a specific model/part number of timer and contactor that I could buy online.
#8
Here is the contactor I would recommend.... EATON C25dnf240a
amazon/C25dnf240a-Definite-Purpose-Contactor-Terminals/
A good quality 40A 240V contactor with a 120vac coil.
Here is a timeclock.... same one Larry recommended....
Amazon: GE 7-Day On/Off Outdoor Metal Box Timer
And a weatherproof box to house the contactor...
Ipex077664 PVC Junction Box 8" x 8" x 4" - - Amazon
200mmx200mmx130mm Waterproof Plastic Sealed Electric Junction Box Case - Amazon
amazon/Plastic-Electrical-Enclosure-Junction-250x200x100/weatherproof box
amazon/C25dnf240a-Definite-Purpose-Contactor-Terminals/
A good quality 40A 240V contactor with a 120vac coil.
Here is a timeclock.... same one Larry recommended....
Amazon: GE 7-Day On/Off Outdoor Metal Box Timer
And a weatherproof box to house the contactor...
Ipex077664 PVC Junction Box 8" x 8" x 4" - - Amazon
200mmx200mmx130mm Waterproof Plastic Sealed Electric Junction Box Case - Amazon
amazon/Plastic-Electrical-Enclosure-Junction-250x200x100/weatherproof box
#9
Is this pump above ground,is it thermally protected? 1 pump with 2 30 amp 2 pole breakers?something seems odd, can you post pic's of that setup?
Geo
Geo
#10
1 pump with 2 30 amp 2 pole breakers?something seems odd, can you post pic's of that setup?
#11
I guess I took that for granit,but still would be nice to know if it is a submersible , if not is it thermally protected ,that would help determine the type of control necessary.
JMO
Geo
JMO
Geo
Last edited by Geochurchi; 01-20-15 at 09:36 AM. Reason: Grammar correction
#12
if not is it thermally protected ,that would help determine the type of control necessary.
You may be able to get away with a definite purpose contactor rather than a full blown starter.
#13
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Pump info
The pump is a 5 hp submersible at approximately 60 feet. I believe the circuit breakers are single pole breakers, but I'm not an electrician, so I can't say for sure.
#14
Are these breakers inside a dry location?first change the single breakers to a 2 pole 30amp,assuming this is in a dry location you could use a controller such as this,gives a little more motor protection
http://www.amazon.com/Magnetic-Start...B004TGTU0W,and a time clock such as this.Amazon.com : Intermatic T101 24 Hour Dial Timer, Indoor Only : Swimming Pool Heater And Heat Pump Parts : Patio, Lawn & Garden
Post a pic of the breakers
Geo
http://www.amazon.com/Magnetic-Start...B004TGTU0W,and a time clock such as this.Amazon.com : Intermatic T101 24 Hour Dial Timer, Indoor Only : Swimming Pool Heater And Heat Pump Parts : Patio, Lawn & Garden
Post a pic of the breakers
Geo