120v from hot to ground on receptacle ?


  #1  
Old 01-21-15, 01:40 PM
M
Member
Thread Starter
Join Date: Dec 2014
Posts: 21
Upvotes: 0
Received 0 Upvotes on 0 Posts
120v from hot to ground on receptacle ?

Changing out outlets in the add on room, and found an outlet that will read 120 from the hot to ground and 120 hot to netural. Even hot to the metal j box gives ke 120 reading. Is this ok ? The only outlet so far in the house that does that. The wiring in this room is ypdated, it has 2 wire with a bare ground wire. Rest of the house is 1951 2 wire, no ground.
 
  #2  
Old 01-21-15, 02:24 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Those are the correct readings for a correctly installed branch circuit with ground.
 
  #3  
Old 01-21-15, 02:33 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
As Ray posted, that is the way it should be. It also means that all of the rest of your receptacles should either be two-prong (no equipment ground connection) or they should be fed from a GFCI (ground fault circuit interrupter) which could be a GFCI receptacle properly wired or a GFCI circuit breaker. Any GFCI receptacle that does not have a proper equipment grounding conductor must be labeled No Equipment Ground.
 
 